Ok
The boiler requires a permanent live, neutral, cpc, switched live and a pump over-run.
inside the honeywell wiring centre you generally have a link between terminals 12 and 13 and another between 13 and 14
This is before you put any of your cables into the wiring centre. Did you remove these links and then just put one between 14 and 12?
If you have not then with your pump still running once the boiler has fired initially it will cause the boiler to carry on firing.
Hope i am making sense as i tend to waffle a bit
From the sound of this there could be a frost stat set too high or linked out if the system is running all the time
LS is live supply to your wiring centre for your external controls-timeclock/roomstat etc
LR is live return to your boiler
Manufacturers like you to take your feed to the boiler first
lucky to get away with reversed polarity not killing the pcb,if it was a baxi new board time
normally reversed polarity effects the detection /ionization circuits so it generally wont detect ignition and go to flame failure sounds like no damage has occurred to your pcbREALLY , gosh i did worry this would of happened..What actually happens to pcb if fried , i mean does it just not fire or could it just be certain functions not work...cos i mean it all seems to function a ok. but maybe there some elements to system i not aware of that been damaged...would hate to leave customer with a issue that should of been attended to now.....i not a bodge it a scarp per type guy... I break i pay .....
yes most boilers suffer the same way,and no biasi are not related to baxi most boilers will have a Honeywell, Siemens,thermowatt pcb honeywells prone to damage with reversed polarity Siemens not so honeywells can sometimes get a soaking,dry out and work,where as Siemens die instantly with the last brand thermowatt just looking at that one will cause it to burst into flames LOL most aristons have this makeOut of interest Are biasi same story....they nothing to do with baxi are they?