Rewiring upstairs lighting circuit

Discuss Rewiring upstairs lighting circuit in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
3
Hi everyone,
I am to rewire the upstairs lighting circuit as the old switches, pendants and cables are outdated.
The existing consumer unit is old but still has mcb's rather than rewirable fuses, but NO RCD protection.

The first question is, does the new replacement circuit HAVE to be RCD protected? I'm pretty sure it does, as my new cables will be chased in to the walls but NOT 50mm deep (obviously in prescribed zones)

Second question, rather than put a whole new CU in as this may introduce problems with the other circuits, would it be good practise to mount a small garage CU next to the existing CU? This garage CU would have a 30Ma RCD and space for two mcb's.

Third question is, what would be a suitable way of feeding the garage CU? And a suitable means of isolation?
My thoughts were to double up the tails in to the load side of the main isolator with the existing CU and to terminate the earth in to the earth bar in the existing CU.
Another option which is possible would be to split the existing tails between the 100 fuse and the existing CU and surface clip to the garage CU roughly a meter away.The flaw in this is that I would have to remove the main fuse, which is obviously bad practise.

Thank you in advance for any advice :)
 
By the time you've messed around doing all that it will be quicker and cheaper just to change the CU as your going to rewire the up stairs lighting Circuit you should not have byroad neutrals, as for the main fuse just pull it out or get the DNO to pull and put it back in when your done
 
If the customer isn't going to go for new fuseboard/ bonding etc- feed a fused RCD spur from the current mcb that currently does the upstairs lights- then supply your re-wired upstairs lighting circuit by the new fused RCD unit- therefore it provides additional protection and o/c protection then just issue a EIC for the 1 circuit.
 
Last edited:
Thanks for the fast responses!
I definitely don't want to go down the route of the new CU as I'm on a short time scale and if problems occur because of the old wiring on the other circuits I haven't got time to sort it.
The most suitable option for me sounds like going from the existing old mcb with a 1.5 t/e, in to the rcd fused spur with a 5A fuse in it, on to the upstairs lighting

Would this be deemed as good workmanship?
 
Before you do a CU change you would have tested everything so will know if a problem exists and then can Factor that in to your time scale, I'm not saying you have to change the CU but I just think at the end of day if your re-wiring up stairs lights in stead of messing about do it right that Way when they get you back to re-wire the next Circuit it will be a lot easer for you
 
If the 13A fuse is in the RCD FCU will there not be a diversity issue as the new RCD FCU will be fed by the current 6A upstairs MCB?

May have mis-read above so ignore me if I have

Dan
EVEN WITH A 5a FUSE, YOU WILL GET DISCRIMINATION PROBLEMS AS THE 6a mcb WILL MOST LIKELY GO FIRST.
 

Reply to Rewiring upstairs lighting circuit in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock