Hi everyone,
I am to rewire the upstairs lighting circuit as the old switches, pendants and cables are outdated.
The existing consumer unit is old but still has mcb's rather than rewirable fuses, but NO RCD protection.

The first question is, does the new replacement circuit HAVE to be RCD protected? I'm pretty sure it does, as my new cables will be chased in to the walls but NOT 50mm deep (obviously in prescribed zones)

Second question, rather than put a whole new CU in as this may introduce problems with the other circuits, would it be good practise to mount a small garage CU next to the existing CU? This garage CU would have a 30Ma RCD and space for two mcb's.

Third question is, what would be a suitable way of feeding the garage CU? And a suitable means of isolation?
My thoughts were to double up the tails in to the load side of the main isolator with the existing CU and to terminate the earth in to the earth bar in the existing CU.
Another option which is possible would be to split the existing tails between the 100 fuse and the existing CU and surface clip to the garage CU roughly a meter away.The flaw in this is that I would have to remove the main fuse, which is obviously bad practise.

Thank you in advance for any advice :)
 
By the time you've messed around doing all that it will be quicker and cheaper just to change the CU as your going to rewire the up stairs lighting Circuit you should not have byroad neutrals, as for the main fuse just pull it out or get the DNO to pull and put it back in when your done
 
If the customer isn't going to go for new fuseboard/ bonding etc- feed a fused RCD spur from the current mcb that currently does the upstairs lights- then supply your re-wired upstairs lighting circuit by the new fused RCD unit- therefore it provides additional protection and o/c protection then just issue a EIC for the 1 circuit.
 
Last edited:
Thanks for the fast responses!
I definitely don't want to go down the route of the new CU as I'm on a short time scale and if problems occur because of the old wiring on the other circuits I haven't got time to sort it.
The most suitable option for me sounds like going from the existing old mcb with a 1.5 t/e, in to the rcd fused spur with a 5A fuse in it, on to the upstairs lighting

Would this be deemed as good workmanship?
 
Before you do a CU change you would have tested everything so will know if a problem exists and then can Factor that in to your time scale, I'm not saying you have to change the CU but I just think at the end of day if your re-wiring up stairs lights in stead of messing about do it right that Way when they get you back to re-wire the next Circuit it will be a lot easer for you
 
Just explain to the customer the different options and the advantages/disadvantage of doing it that way- and then its up to them- you can only give them your opinion
 
I would probably put RCD FCU in as it's easiest - Have you checked to see if you can replace the MCb with RCBO?

I did think about that bit not sure of the compatability due to the age of the existing board. However before I start the job ill get a look in at what make the board is and try and find one that fits. If that fails the the RCD fcu is the next option.
 
If the 13A fuse is in the RCD FCU will there not be a diversity issue as the new RCD FCU will be fed by the current 6A upstairs MCB?

May have mis-read above so ignore me if I have

Dan
 
If the 13A fuse is in the RCD FCU will there not be a diversity issue as the new RCD FCU will be fed by the current 6A upstairs MCB?

May have mis-read above so ignore me if I have

Dan
EVEN WITH A 5a FUSE, YOU WILL GET DISCRIMINATION PROBLEMS AS THE 6a mcb WILL MOST LIKELY GO FIRST.
 
i'd not bother. stick a 13A fuse in as the cable is adequately protected by the 6A MCB
 
And if your planning of re wiring the whole circuit anyway (new circuit from db) bonding will need to be in place anyways and to issue a eic regardless of upgraded the db or not.￾
 

Reply to Rewiring upstairs lighting circuit in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi fellow sparks, I've just started out on my own so I'm spending a lot of my time trying to find out the correct way of doing things of...
Replies
13
Views
846
I have been asked to change cu from old fuse board which has 6 fuses. Only 4 fuses are used. The first fuse feeds cooker circuit. This is not used...
Replies
17
Views
819
In a property with two consumer units one for the ring main etc., and the other for the 1970s storage heaters (storage heater CU looks like it’s...
Replies
14
Views
1K
Hi all, I am looking for some advice regarding old rewireable (3036) fuse boards in regards to additions and alterations. I am an electrician and...
Replies
28
Views
4K
Good day. First time poster. We recently had an electrician perform the EICR, as this is a newly purchased property I thought'd I would have the...
Replies
7
Views
707

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock