Ahh, I see your point!
Discuss Rewiring upstairs lighting circuit in the UK Electrical Forum area at ElectriciansForums.net
I would probably put RCD FCU in as it's easiest - Have you checked to see if you can replace the MCb with RCBO?
Just explain to the customer the different options and the advantages/disadvantage of doing it that way- and then its up to them- you can only give them your opinion
EVEN WITH A 5a FUSE, YOU WILL GET DISCRIMINATION PROBLEMS AS THE 6a mcb WILL MOST LIKELY GO FIRST.If the 13A fuse is in the RCD FCU will there not be a diversity issue as the new RCD FCU will be fed by the current 6A upstairs MCB?
May have mis-read above so ignore me if I have
Dan
EVEN WITH A 5a FUSE, YOU WILL GET DISCRIMINATION PROBLEMS AS THE 6a mcb WILL MOST LIKELY GO FIRST.