When you do the continuity test on a ring final circuit and you have to connect L1 to N2 and vice versa, this assumes you know which L cable is the incoming or outgoing.
I understand that if you connect L1 to N1 and vice versa the ohm readings rise then fall as you go round the ring circuit. Why is this? I can't explain this to a friend who asked.
If the connections are done correctly the readings stay the same as you go round.
Thanks
I understand that if you connect L1 to N1 and vice versa the ohm readings rise then fall as you go round the ring circuit. Why is this? I can't explain this to a friend who asked.
If the connections are done correctly the readings stay the same as you go round.