if it goes out and back ( as a ring) then it will be double the length, as long as it takes the same route back. not if it returns via istanbul though.
 
if im running 4c 25mm swa from service fuse to new dis board(20M) and plan to run single core earth along side, what size do i need .. tn-c-s 0.07 ze....

calculator out in car, i would just run a 16mm but can i get away with 10mm along with armour????
 
Wired a three story house in four 32A 4mm radials as oppose to 32A rings, I really wished I hadn't, cost more, longer to run and had trouble with max Zs despite no faults found , had to knock it to 20A in the wbd
 
What size cpc is in 4mm? Is it 2.5mm?


Can't answer because the forum thinks the answer is too short
icon7.png
 
as for 4mm radials ived devided it up and none will be over 40m using 26A as Ib...

yes 5core swa it is but was thinking maybe cheaper to just run 16mm alongside maybe 10mm
 
3p/N use 5 core.
Dedicated earth and Swa as belt and braces in case some idiot decides to guess at how to make an Swa gland off...........as Wade's post this week.

oops.............wade just posted the photo honest he didn't really make that end off:)) lol
sorry mate hahahaha
 
Last edited by a moderator:
5 core swa
4 core will suffice using armouring as your cpc mate as long as you gland it correctly and it passes all the relevant tests as the guys have already stated..............me.................5 core every time and dedicated earth core bolted and bonded and earthed to everything with 6mm brass nuts and bolts:)
 


That Earthingnuts pdf is more confusing than useful, far better to use this table when dealing with SWA CPC values and compliance's



Blue = min CSA of cables SWA to comply.

(Red) = Cable does not comply.

Table for 70[SUP]0[/SUP]C Thermoplastic PVC SWA cables.

Conductor CSA
Minimum CSA of SWA to meet 54G
CSA of armour 2 core
CSA of armour 3 core
CSA of armour 4 core
1.5
3.4
15
16
17
2.5
5.7
17
19
20
4
9.0
21
23
35
6
13.6
24
36
40
10
22.6
41
44
49
16
36.1
46
50
72
25
36.1
60
66
76
35
36.1
66
74
84
50
56.4
74
84
122
70
79.0
84
119
138
95
107.2
122
138
160
120
135.3
(131)
150
220
150
169.2
(144)
211
240
185
208.6
(201)
230
265
240
270.6
(225)
(260)
299
300
338.3
(250)
(289)
(333)
400
403.9
(279)
(319)
467



Table for 90[SUP]0[/SUP]C Thermosetting SWA cables operating at 70[SUP]0[/SUP]C.

Conductor CSA
Minimum CSA of SWA to meet 54G
CSA of armour 2 core
CSA of armour 3 core
CSA of armour 4 core
1.5
3.4
16
17
18
2.5
5.7
17
19
20
4
9.0
19
21
23
6
13.6
22
23
36
10
22.6
26
39
43
16
36.1
41
44
49
25
36.1
42
62
70
35
36.1
62
70
80
50
56.4
68
78
90
70
79.0
80
90
131
95
107.2
113
128
147
120
135.3
(125)
141
206
150
169.2
(138)
201
230
185
208.6
(191)
220
255
240
270.6
(215)
(250)
289
300
338.3
(235)
(269)
(319)
400
451.0
(265)
(304)
452
 
well i dont even need the extra core , but any job most of time i notice one tied to it but if i can get 5c which table dosent metion well

salt laden area sea front
 
i=p/u

I'm coming over to Northern Ireland on tonight's ferry.
My genius and intellect comes cheap at as much Guinness and smokes I can consume each evening after work.
PM me for phone number.
 
well i dont even need the extra core , but any job most of time i notice one tied to it but if i can get 5c which cable dosent metion well

salt laden area sea front

Then i would personally run your SWA cable underground in a duct, sealed at both ends with a propriety duct seal compound. And make sure you pull the cable into the duct carefully, any damage to the sheath, will allow the salt laden water to corrode the SWA very quickly!! lol!!
 
i punched hole through ceiling and uncovered a beam , supposed to be holding building up, didnt look to healthy

the cable is inside but so is beam
 

Reply to ring v radial in the Electricians' Talk area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock