if it goes out and back ( as a ring) then it will be double the length, as long as it takes the same route back. not if it returns via istanbul though.
 
if im running 4c 25mm swa from service fuse to new dis board(20M) and plan to run single core earth along side, what size do i need .. tn-c-s 0.07 ze....

calculator out in car, i would just run a 16mm but can i get away with 10mm along with armour????
 
Wired a three story house in four 32A 4mm radials as oppose to 32A rings, I really wished I hadn't, cost more, longer to run and had trouble with max Zs despite no faults found , had to knock it to 20A in the wbd
 
What size cpc is in 4mm? Is it 2.5mm?


Can't answer because the forum thinks the answer is too short
icon7.png
 
as for 4mm radials ived devided it up and none will be over 40m using 26A as Ib...

yes 5core swa it is but was thinking maybe cheaper to just run 16mm alongside maybe 10mm
 
3p/N use 5 core.
Dedicated earth and Swa as belt and braces in case some idiot decides to guess at how to make an Swa gland off...........as Wade's post this week.

oops.............wade just posted the photo honest he didn't really make that end off:)) lol
sorry mate hahahaha
 
Last edited by a moderator:

Reply to ring v radial in the Electricians' Talk area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock