Discuss How do I know if I've got a ring circuit or a radial circuit? in the UK Electrical Forum area at ElectriciansForums.net

A ring circuit you can test continuity on Live Neutral Cpc conductors @ the CU or @ the power points.
Radial circuit checking r1 r2 by linking these conductors @ the end of the radial circuit
 
In most cases if the supply breaker is 32A it is an RFC, and if 20A/16A a radial. But there can be exceptions to that by design, or by someone (typically builder or DIY) breaking an otherwise good design.

If you have a socket out (power off and tested to be off obviously!) with two sets of wires at the back of it and you isolate them there, then if measuring L-L or N-N you see a low resistance of under a few ohms then it is almost certainly an RFC.

Measuring CPC-CPC (earth - earth) should also form a loop, but in is not uncommon for the CPC of circuits to be linked elsewhere back to the main earth terminal, such as at a boiler, so that test is not as reliable as checking L-L and N-N.

If you find one of L-L & N-N is linked but not the other then you have a fault somewhere to be found and fixed!
 
Radial circuit has only one wire coming out of the CU from the MCB usually, a Ring circuit has two, but this does assume there are not two radials on one MCB.
That is the key word!
The breaker size sets expectations.
The number of wires set expectations.

But ultimately only testing confirms what is actually the case.
 

Reply to How do I know if I've got a ring circuit or a radial circuit? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Currently planning a new rewire for my kitchen and want to get things right first time when it comes to appliances consumptions and circuits...
Replies
0
Views
969
Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
Replies
12
Views
671
For some Strange reason we have three Circuits running in the Kitchen i think for two OLD Cookers and a Ring Circuit for the house. Well the...
Replies
18
Views
2K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
631

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock