Discuss Running electric to island. in the UK Electrical Forum area at ElectriciansForums.net

Steviecuk

-
DIY
Reaction score
29
Hi all.

I'm currently building an island in my kitchen which will contain a gas hob. I've cut a trench about 60mm wide from the edge wall to where I want everything popping up.

Plumber will be fitting a 22mm gas pipe wrapped in Denso tape before it is filled in with screed and then tiled.

My question is can I run my twin and earth in conduit in the same trench as the gas? I was thinking maybe with a spacer in there so the screed will create a barrier between them? Obvs each respective trade will do the work but just getting ideas if I need to did another bloody channel.

Thoughts and ideas please.

Thanks. S.
 
My question is can I run my twin and earth in conduit in the same trench as the gas?
Yes.

The On Site Guide says two things about gas pipes and separation.
Min distance from supply equipment, meters, consumer units etc. (150mm)
Min distance from switches, sockets, and electrical supply and distribution cables (25mm)
It also talks about interposing an insulating material if you can't do that.

It doesn't sounds like you have either of those cases, and in any case you are in conduit.
 
I would run singles in a 25mm flexible conduit rather than T&E easier to replace if needed, pulling one out attached to the new length of single.
 
Yes.

The On Site Guide says two things about gas pipes and separation.
Min distance from supply equipment, meters, consumer units etc. (150mm)
Min distance from switches, sockets, and electrical supply and distribution cables (25mm)
It also talks about interposing an insulating material if you can't do that.

It doesn't sounds like you have either of those cases, and in any case you are in conduit.
Thanks for your replies. Unfortunately It's just been blown out of the water by the plumber. It's against gas regs apparently. Took bloody ages to dig that channel. And the mess... OMG the mess. Will have to do another I guess. 🤦🏻‍♂️
 
Thanks for your replies. Unfortunately It's just been blown out of the water by the plumber. It's against gas regs apparently. Took bloody ages to dig that channel. And the mess... OMG the mess. Will have to do another I guess. 🤦🏻‍♂️

Ask the plumber to show you where in the gas regulations it says that this isn't allowed.

This page from the gas safety register says that 25mm separation is required or an insulating barrier (conduit complies as an insulator, also the layer of denso tape should count) Can we help you? Part 2 - Registered Gas Engineer - https://registeredgasengineer.co.uk/technical/can-we-help-you-part-2/#:~:text=Q%3A%20What%20are%20the%20distances,in%20BS%206891(1).
 
Can they provide a gas reg? Or is it just that they don’t want to do it that way?
it might be worth asking another gas engineer
To be honest I didn't ask for the reg. just said it was against them and assumed it would be right. But if you think differently I'll definitely ask another as it'll save so much work. 👍🏻
 
To be honest I didn't ask for the reg. just said it was against them and assumed it would be right. But if you think differently I'll definitely ask another as it'll save so much work. 👍🏻
Actually I wouldn't make a rod for your own back unless the gas fitter will be the one filling the hole (which I doubt!)
Just go along with it, let him do his gas thing.
Then sort out the electrics in line with the electrical guidelines which definitely allow this.
Then fill the hole.

I've just asked my pal the (Gas safe) gas man and he agrees that if insulated it doesn't even begin to be an issue.
 
Ask the plumber to show you where in the gas regulations it says that this isn't allowed.

This page from the gas safety register says that 25mm separation is required or an insulating barrier (conduit complies as an insulator, also the layer of denso tape should count) Can we help you? Part 2 - Registered Gas Engineer - https://registeredgasengineer.co.uk/technical/can-we-help-you-part-2/#:~:text=Q%3A%20What%20are%20the%20distances,in%20BS%206891(1).
Sorry Dave didn't see that you'd also replied with the link. Bang on. I'll have a word with him, he might have got the wrong end of the stick when I was talking to him. Cheers guys. 👍🏻
 
Actually I wouldn't make a rod for your own back unless the gas fitter will be the one filling the hole (which I doubt!)
Just go along with it, let him do his gas thing.
Then sort out the electrics in line with the electrical guidelines which definitely allow this.
Then fill the hole.

I've just asked my pal the (Gas safe) gas man and he agrees that if insulated it doesn't even begin to be an issue.
Wow all so helpful thank you very much. Sounds good to me. Thank you.
 
I suspect from the fact that they are going to wrap the pipe in denso tape that the plumber is either older or trained by an older plumber and hasn't kept up to speed with current methods.

As far as I know denso tape isn't the preferred method any more, the preference is plastic coated copper pipe.
 
once did a raft of million pound new builds where the plumber laid his gas to the island and the sparks would tie wrapped a 2.5 to the gas pipe for the isalnd sockets. plumbers came back and pulled all the cables out

no wonder sparks hate plumbers
 
once did a raft of million pound new builds where the plumber laid his gas to the island and the sparks would tie wrapped a 2.5 to the gas pipe for the isalnd sockets. plumbers came back and pulled all the cables out

no wonder sparks hate plumbers

Tie wrapping your cables to the gas pipe is a bit naughty though!
 

Reply to Running electric to island. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello guys, It’s my first post here so please be gentle :) I’m having a kitchen extension done and will have the hob and few powerpoints...
Replies
4
Views
1K
I'll start by saying - I have absolutely no intention of doing any wiring or anything electrical myself. You get someone professional to do a...
Replies
8
Views
860
First time DIY post here…. My wife and I bought an old, run down 70’s lake trailer and ran into an AC wiring issue. Our thermostat is wired...
Replies
3
Views
722
Hi All, We have an old Country villa in Spain. The housing electrics were not good so the house recently has been completely re-wired to a good...
Replies
2
Views
760
I really hope someone can help me. Last July I got an electricity bill showing an enormous rise in my kwh consumption of about 900% from what it...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock