Hi all

OK..did a cu change yesterday .. old wylex with an external rcd for a new amd3 dual rcd cu.

This morning the customer rings to say the shower has tripped the rcd.
Turn up on site..and the rcd that has tripped is not the one that the shower circuit is on.!
So i check for crossed over neutrals .. none.
i check with 500v IR test for connections between circuits between each rcd..none.

So.. the rcd only trips if the shower is running .. so i remove 1 element to check its not breaking down...all ok.

swap the elements ..all ok..

But any time both elements work together the rcd trips.

Put a clamp meter on the shower earth .. leakage just 8mA.

Ok ..im a bit stumped now...of course some interaction is going on between the 2 rcd's circuits .. but i cant measure any connection between them.

The install is in an old farm house 4 other dwellings around it all with TT systems including the 1 im working on.

Local supply transformer is in the field right next to the job .

All and any idea's please .

Many thanks in advance.

Vito
 
Hi all

OK..did a cu change yesterday .. old wylex with an external rcd for a new amd3 dual rcd cu.

This morning the customer rings to say the shower has tripped the rcd.
Turn up on site..and the rcd that has tripped is not the one that the shower circuit is on.!
So i check for crossed over neutrals .. none.
i check with 500v IR test for connections between circuits between each rcd..none.

So.. the rcd only trips if the shower is running .. so i remove 1 element to check its not breaking down...all ok.

swap the elements ..all ok..

But any time both elements work together the rcd trips.

Put a clamp meter on the shower earth .. leakage just 8mA.

Ok ..im a bit stumped now...of course some interaction is going on between the 2 rcd's circuits .. but i cant measure any connection between them.

The install is in an old farm house 4 other dwellings around it all with TT systems including the 1 im working on.

Local supply transformer is in the field right next to the job .

All and any idea's please .

Many thanks in advance.

Vito
2nd Paragraph last two lines, what exactly do you mean by that statement? Agree with Strima could be loose N connection.
 
Are the white appliances (dishwasher, tumble dryer, washing machine, microwave) or electric hob (is it an induction hob?) - supplied by the RCD which trips?

Could you measure the L-E, N-E and L-N voltages at the CU main switch with the shower off and then on (all mcbs apart from shower one off) and let us know them? Shower on full flow and high heat so elements remain on.
 
Last edited:
Another possibility, curtsey of @Richard Burns
ne-fault-rcd-trip-on-current-use-jpg.44332
 
Neutrals in the cu .. all of them...are good.

Accumulated leakage ... wrong rcd for this.!

Cooker and kitchen ring circuit with all appliances is on the rcd that's tripping .. but that's not the one with the shower on it.
No induction hob..

Global IR test .. well the lowest IR for any of the circuit's is 60 meg ohms .. ..but the shower circuit is 999meg ohms.

Midwest... Yeh .. I've had this before ... but so far none of the circuit's on the tripping rcd side seems to have a significant neutral earth fault.

But so far I think this will be my next point of investigation. ..if only because I can't think of another.

Marcoi .. I could .. but what are you getting at with this..?

Thanks again for the input guys

Vito
 
Had exactly the same once turned out tncs system loose n in metre witch had recently been changed dam metre monkeys witch in turn under high load shower ect the high resistance made earth lower potential than n return try clamp metre on gas and water while shower is on or voltage indicator
 

Reply to SHOWER TRIPS RCD ITS NOT CONNECTED TO in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
406
Hi all, There's 2 single fan ovens in the house my mother recently moved into. Posh elecronic AEG units. It's been sat empty for a year, so the...
Replies
19
Views
2K
An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
884
Hi all. Sort of an interesting one. I had a call from a client to say she is getting a shock when using the shower. I told her not to use it and...
Replies
15
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock