Search the forum,

Discuss Solar panel circuit MCB size? in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

no it doesn't require an RCD.

The inverter manufacturers give specifications for RCD fitting where required by local regulations - ie where required by BS7671, so an RCD is only needed where it's required under BS7671.

All you're doing is adding a source of nuisance tripping to the system by adding an RCD where it's not needed.
Thanks Gavin, To comply with BS7671 though, if the solar panel circuit is wired pvc t+e cable and buried within the plasterwork (less than 50mm) it must be protected by a 30Ma RCD. As far as I can see, no choice in the matter. Are ALL your LV circuits wired on the surface? Thanks
 
I think you will find outside is a special location that requires RCD protection. All manufactures instructions on systems I have fitted have stated it requires RCD protection. Also I said I install a seperate board for PV with its own RCD, to prevent nuisance tripping on the domestic circuits. The MCS guy also confirmed that a RCD is a requirement on my annual inspections
 
Yes solar PV should be protected by an RCD. Some manufacturers state 30Ma some state 100Ma. The solar array is outside, usually roof mounted so it requires RCD protection. I always install a new 2 way RCD board separate from the domestic CU to avoid nuisance tripping. The PV installation can have quite a lot of earth leakage and if it's connected to the same RCD as the house it can cause problems. Separating the two installations can make life a lot easier with regard to nuisance tripping.
Thanks Rico, what I was planning was that the Solar panel circuit be wired on its own RCBO circuit, which is basically what you have been doing. I'm not into solar panel wiring, this is just a one off. Why do you install a 2 way unit? Thanks
 
I install a 2 way board for the PV so the combined earth leakage from the house and PV doesn't cause problems. I cut the tails and put Henley blocks on them. This way my house CU and PV CU are separate. So the earth leakage from the house and PV doesn't combine to trip RCD's. The PV earth leakage can be quite high so i tend to put that on its own RCD as recommended in the manufactures instructions. I have been called out to lots of installations that are tripping because they have not been installed this way. I change it to this method and all is solved. Easier for testing too.
 
I install a 2 way board for the PV so the combined earth leakage from the house and PV doesn't cause problems. I cut the tails and put Henley blocks on them. This way my house CU and PV CU are separate. So the earth leakage from the house and PV doesn't combine to trip RCD's. The PV earth leakage can be quite high so i tend to put that on its own RCD as recommended in the manufactures instructions. I have been called out to lots of installations that are tripping because they have not been installed this way. I change it to this method and all is solved. Easier for testing too.
Yes, I understand your thinking hence I've gone separate RCBO's for each circuit. Just wondering why you put a 2 way unit in. Do you mean that the RCD + MCB takes the 2 ways up? Or you require 2 x circuits for your systems?
 
I think you will find outside is a special location that requires RCD protection. All manufactures instructions on systems I have fitted have stated it requires RCD protection. Also I said I install a seperate board for PV with its own RCD, to prevent nuisance tripping on the domestic circuits. The MCS guy also confirmed that a RCD is a requirement on my annual inspections
I think you'll find that the outside bit is DC, and your RCD has nothing to do with that side of the inverter - the RCD wouldn't trip if there were a fault on the DC circuit, how could it?

The inverters are either galvanically isolated, or transformerless with an integral RCMU unit to protect them.

what the MCS guy said says more about the substandard nature of the MCS inspection system than it does the reality of what's required.
 
Thanks Gavin, To comply with BS7671 though, if the solar panel circuit is wired pvc t+e cable and buried within the plasterwork (less than 50mm) it must be protected by a 30Ma RCD. As far as I can see, no choice in the matter. Are ALL your LV circuits wired on the surface? Thanks
or use earthed metal capping, but yes an RCD would be one way of protecting the circuit in that situation.

If the inverter is in the loft we mainly run SWA surface mounted externally in retrofit installations to avoid disturbing the internal decor, having to pull carpets up etc.
 
I think you will find outside is a special location that requires RCD protection.

I don't think you will.

'Outside' in general isn't a special location or installation. Some specific situations, such as swimming pools, agricultural, etc. are.

In a normal domestic situation, it's only socket outlets outside that require RCD protection, not distribution circuits, lighting, etc.
 
I think you'll find that the outside bit is DC, and your RCD has nothing to do with that side of the inverter - the RCD wouldn't trip if there were a fault on the DC circuit, how could it?

The inverters are either galvanically isolated, or transformerless with an integral RCMU unit to protect them.

what the MCS guy said says more about the substandard nature of the MCS inspection system than it does the reality of what's required.
yup, ive seen 700v on some strings on bigger solar panel jobs.

only a positive and negative from solar panels so no where to connect an earth after the inverter anyway

we are talking multiple TP inverters in one room here
 
Yes solar PV should be protected by an RCD. Some manufacturers state 30Ma some state 100Ma. The solar array is outside, usually roof mounted so it requires RCD protection. I always install a new 2 way RCD board separate from the domestic CU to avoid nuisance tripping. The PV installation can have quite a lot of earth leakage and if it's connected to the same RCD as the house it can cause problems. Separating the two installations can make life a lot easier with regard to nuisance tripping.

what has the RCD in your 2-way consumer unit got to do with the DC side of things= NOTHING lol

and i can probably rest assure you are not fitting type b RCD's as you dont have to!
 
Rihco what a load of tish! It does not require RCD protection at all, we always design the RCD out so surface mounted or alike then no nuisance tripping can occur. An inverter can cause nuisance tripping on its own RCD as well I've seen it, and changed it. RCDS with solar PV Is usually poor design Tbh
 
I follow manufacturers instructions. And also the MCS inspectors have instructed us to it this way.
You've misread the instructions, and the MCS inspector doesn't know what he's talking about - many of them don't.

I had one attempting to insist that I should have earth bonded the array frame on an isolating transformer inverter system under the old rules about bonding the frames for TL inverters only. He was a former gas fitter who'd never installed a solar PV system.
 
If regulations in the country of installation stipulate an external residual current device, you must use
a device with a tripping threshold of 100 mA or more.
that's SMA's instructions relating to RCDs.
 
The head technical person from one of the MCS schemes rang me one time a while back because I'd had a pop at their assessors on here (if I remember right).

They were of the opinion that their assessors really knew what they were doing because they made sure they'd all done a minimum of 5 solar PV installations before they'd give them a job as an assessor.

IIRC I pointed out that our apprentice had done around 100 installs.

Boils my **** that they all consider it acceptable to have folk assessing us who we'd not class as competent to even supervise the most basic of domestic installs*.

Apparently this isn't something that can be discussed at MCS though, 'it's an enforcement issue'.



*not tarnishing all assessors with the same brush, there are some highly competent assessors out there as well, it's just the minimum standards that are set far too low.
 

Reply to Solar panel circuit MCB size? in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top