80amp main switch RCD, occasionally trips when a couple of circuits are switched on (doesn't matter which circuits) with nothing plugged in.

IR tests all good. Replaced RCD for new. Happens in all weather ( don't think its external )

Only sockets on this consumer unit.

Ive had my guys out at it twice with no joy. New build wiring from 16th edition.

Im going to investigate myself this week, Im sure Ive had loose connections causing tripping before, it about all I can think of, a loose tail somewhere around the main switch.


Anything else to look out for ?

Im pretty certain its not a dodgy nail at floorboard etc its fairly new property and in good condition with chipboard throughout.
 
This thread has now had nearly 5000 views , would you believe , seems like most could be in the north / Glasgow area , bloody hell ...

Look Jamie you are famous some us can only dream of reaching such hypnotic heights, please don't LEAF
 
I have isolated the fault to an area of a room but there is no access at all !

I know there is always a logical explanation for faults but given the size of the property and how unorganised it is its completely unrealistic for anyone to suggest they would find it in a day,without seeing it as they have been claiming!


Earth leakage meter is not something Ive needed before, our installs are almost all brand new and tested accordingly

As mentioned before i wouldn't normally delve into fault finding this much but I've kind of inherited this problem.


It's ''NOT'' completely unrealistic to find a RCD fault within a day, an experienced electrician used to fault finding, would have little to no problem tracing out the cause of that fault in a domestic setting.

That last paragraph above, should be telling you WHY an experienced electrician will find the fault, while you will have trouble finding the fault!!!

RCD's are here to stay, no matter what type of installs you normally do or don't do. A leakage clamp tester should now be seen as an essential part of any electricians test kit. MFT RCD testing, is fine for new RCD breakers, but when it comes to fault finding Nope!! Ramp testing with a MFT can only give you very limited information, whereas a leakage clamp can lead you directly to the source of a leakage problem....
 
I can just picture Trev caning it up to Glasgow in a mucky yellow robin reliant with $$$ signs in his eyes singing fog on the tyne.
 
I'm just bumping some of the older threads in the general electrical forum that had a lot of replies. They might not be current topics, if they're not, just ignore them and they'll soon drop off the list. If you DO wish to add a reply and get the conversation going again, feel free to do so. Your input might help somebody else in the future.
 
I'm just bumping some threads in the Electrical Forum, don't mind me while I do this, you don't have to respond to them. Although if they are still current topics, and you do wish to reply, you're welcome to. Keep the thread on-topic and make sure you stick to the forum rules though.
 

Reply to Strange RCD Fault in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock