Currently reading:
Surge protection Requirements

Discuss Surge protection Requirements in the UK Electrical Forum area at ElectriciansForums.net

DNS1

-
Esteemed
Reaction score
771
Excuse the probably stupid question!

I'm a bit out of date, so not yet up to speed on 18th edition.

Been prepping for a domestic board change, but am confused about whether I need an SPD or not.

Seeing as the majority of suppliers are selling their boards without the SPD, I'm assuming they're not an absolute requirement, but I'm having a hard time finding something to confirm this.

This is a bog standard domestic set-up, nothing fancy at all, was new build in 2001 so all pretty straightforward.

Can someone point me in the right direction?

Cheers
 
Cheers for the response, unfortunately I don't have the book yet!

Would someone mind sending me a screenshot/photo of the relevant section?
77ECCE0A-6DF5-4712-B40A-B65779CF98BE.jpeg
Here you go
 
Thanks for that...

I'll have to read up on doing the risk assessment...

I wonder if the fact that there are no exposed cables between the house and substation will satisfy the regs... It all seems rather OTT IMO!
 
Hi For what they cost why not?
Phil

I'm just not sure what they achieve!

Unless there is an issue with the supply from the DNO (which will make them liable anyway!) what can they protect against?

There's no chance of a lightning strike as there are no overhead cables between the property and the substation.

If they're that important, why doesn't the DNO have to supply them?
 
You don't need to do the risk assessment for a single dwelling, if you read it closely there is a section about it purely down to cost of protection vs value of the installation.

If the householder doesn't deem it worthwhile, you don't have to install it.

Depending on the cu you are using, it could be a cheap addition, or overly expensive.
[automerge]1585595413[/automerge]
I'm just not sure what they achieve!

Unless there is an issue with the supply from the DNO (which will make them liable anyway!) what can they protect against?

There's no chance of a lightning strike as there are no overhead cables between the property and the substation.

If they're that important, why doesn't the DNO have to supply them?
The real issue is that small surges was never a problem traditionally, however now that most lighting is led, almost all appliances have electronics, etc, then even a small switching surge could cause expensive issues.

From an installers pov, if you do a cu change and then half the led lamps fail 6 months later, you would likely get the blame even though the cu change has nothing to do with it!
 
Last edited:
The thing to remember is you only need to protect against transient overvoltages originating from the distribution network, switching surges from within the installation only need to be considered for protection, this is often mistaken for being a requirement rather than a consideration
 
I'll have to read up on doing the risk assessment...

There are several cases where the new regs say you must, basically anywhere there is any lighting conductor system in use (in that case you also need a Type 1 SPD), a risk to life (e.g. hospital, etc), or risk of a loss of business continuity (so every work place!) but for homes it usually comes down to the "risk assessment".

Realistically some companies (e.g. Fusebox) include a Type 2 SPD as standard now, so you just go with it as no extra effort, and for many others it is under (sometimes well under) £100 for it anyway.

You could argue that mains-powered stuff ought to be competently designed to deal with surges, but sadly that is not the norm in today's cost-cutting world and cheap s**t LED lights and consumer electronics is the norm.
 
I'm just not sure what they achieve!

Unless there is an issue with the supply from the DNO (which will make them liable anyway!) what can they protect against?

There's no chance of a lightning strike as there are no overhead cables between the property and the substation.

If they're that important, why doesn't the DNO have to supply them?

Liability doesn't matter, the DNO being liable won't magically prevent anything from being damaged. No payment in respect of that liability will replace lost data.
The point of the SPD is to protect equipment from surges.

A lack of overhead cables doesn't prevent lightning hitting the substation or the upstream HV lines.

Why would the DNO supply SPD's? RCDs, MCB's, main bonding are all important but the DNO don't supply them!
[automerge]1585649680[/automerge]
I'm a bit out of date, so not yet up to speed on 18th edition.

Then don't do, or design, electrical work until you are. The 18th edition has been in place for over a year now.
 
A lack of overhead cables doesn't prevent lightning hitting the substation or the upstream HV lines.

There is another thread that ended up discussing SPD here:
One of the folks on this forum (Mike Johnson) reported that his Type 2 SPD in France keeps burning out on the end of a SWA cable so in rural cases it looks as if a Type 1 may needed to deal with magnitude of surges on long underground feeds without overhead cables even being a factor.

OK, that region is more lightning prone than most of the UK, and it is odd in that the French provide a TT supply off a SWA cable, so what do they do with the SWA's earth? A discussion for another day...
 
I appreciate my limitations and that I am out of date... It's no longer my full-time job!

I was just curious as suppliers are selling the majority of their consumer units without SPDs, so it got me wondering how necessary they were in real life
 
I appreciate my limitations and that I am out of date... It's no longer my full-time job!

I was just curious as suppliers are selling the majority of their consumer units without SPDs, so it got me wondering how necessary they were in real life

Suppliers are selling off old stock, that's what they do.
They're probably having a hard time shifting the old stock as electricians are unlikely to be fitting it, so they use marketing strategies to make it appear that they selling a lot of non-SPD boards. This manipulates people into buying their non-SPD boards, generally people who don't know the regulations or understand them.

Don't forget, suppliers aren't required to only sell products which give full compliance with the current regulations without the addition of other parts. Suppliers are running a business to sell whatever they can to whoever they can and make money doing so. It is up to the installer to ensure they are complying with the regulations.
 
single dwelling...recommendation only...if the client says no then you dont have to fit one...and why have you not got the 18th edition ..only came out in January 2019
Your phraseology isn't correct. In a domestic situation a risk assessment is required and where it isn't done then an SPD should be fitted unless the total value of the installation does not justify it.

I'm not going to bother with a risk assessment for £30 and if a customer is arguing over £30 then they're not a customer for me.
 
Your phraseology isn't correct. In a domestic situation a risk assessment is required and where it isn't done then an SPD should be fitted unless the total value of the installation does not justify it.

In the first instance a Hazard Analysis should be carried out, if a hazard is identified then the Risk assessment is required.
 

Reply to Surge protection Requirements in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock