Search the forum,

Discuss Taking money for certification - customer dont wanna pay! in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Tell me please, who are these 'most electricians' to whom you refer? I hope you are not suggesting that the vast majority of us are cowboys?
there was damaged cable between box and light pendant so I was really lucky to find the box using my inspection camera and be able to replace a cable without destroying big amount of ceiling. There were just two small holes in the ceiling that has been just renovated two days before.

@GMES: yeah, I know. I think I will talk to her on Monday and we will solve an issue. She is arguing to pay 150 as other electrician told her I cant take money for doing that. But she still needs to pay the rest of price:/ Anyway, I believe we will figure it out and she will pay at least price close to the one agreed at the start.
 
there was damaged cable between box and light pendant so I was really lucky to find the box using my inspection camera and be able to replace a cable without destroying big amount of ceiling. There were just two small holes in the ceiling that has been just renovated two days before.

@GMES: yeah, I know. I think I will talk to her on Monday and we will solve an issue. She is arguing to pay 150 as other electrician told her I cant take money for doing that. But she still needs to pay the rest of price:/ Anyway, I believe we will figure it out and she will pay at least price close to the one agreed at the start.

He's talking absolute rubbish, plus it's nothing to do with him. You can charge for anything you like, especially testing.
Just type out another invoice then with testing and inspection for £0, and add the £150 to labour charge.
 
I've looked at this thread. A marriage made in heaven. You've gone in too cheap, she liked a cheap quote.
You're trying to claw money back for you're mistake.
Provide her with a copy of the test schedule for £0 and put it down to experience.
 
And it could be just how he presented quote, broke price down and she thinks 150 for testing which he should be doin anyway.. But it's just how he presented it.

Am I reading this right...

Like if I was going to wire a small flat and said 2 days each fix and £ 150 for testing instead of adding it into days/hours ...
 
Wow, great thread. You just need to explain that there has been a misunderstanding, take it on the chin and look at getting some invoicing lessons.

For example, at the bottom of my invoices, I have a section labelled 'Testing, certification and building control notification'

For a full cert it's usually £25 or a tenner for a minor works, the customer then knows that

1, They are receiving a cert
2, The work is being notified
3, They have not been 'jobbed' by some cowboy who will tear half the ceiling down, 'like most electricians' and walk off with £150 to boot.
 
Mistery solved. Her boiler has broken, and gas specalist told her Im a retard putting 13amp fuse in cable to boiler and I destroyed the device.
So he blamed me that the boiler got broken and they got no hot water. I went to her and explained I could give a 3amp fuse, it could help to prevet boiler from getting damaged but It is not my fault that it took too much power and a pump blew off.

She understands that now and she said there is no problem to pay me. Looks like I am a little drama queen lol, sorry guys and thans all for your help!
 
Well you are a prat for putting a 13 amp fuse in for a piece of equipment which requires a 3 amp fuse. Doesn't everyone know a domestic gas boiler should be fused at 3 amps? And even if not then it will be in the instructions for the boiler which you read before connecting it I assume?

I hope you made a note on this famous certificate to say that you installed it other than in accordance with the regulations and manufacturers instructions.
 
Well you are a prat for putting a 13 amp fuse in for a piece of equipment which requires a 3 amp fuse. Doesn't everyone know a domestic gas boiler should be fused at 3 amps? And even if not then it will be in the instructions for the boiler which you read before connecting it I assume?

I hope you made a note on this famous certificate to say that you installed it other than in accordance with the regulations and manufacturers instructions.
My bad indeed, but it shouldnt blow because of me!
 
I am so confused! Anyone care to summarise, I have read the whole thread and I have a few questions...

Whats the electricians handbook?

Why wouldn't you put a 30p fuse on the boiler?

Was the faulty boiler why she wasn't paying you or was she not paying you for the Certs?

Surely you have a good hard copy of your quote so if she refused to pay you, you would have a argument in court?

What is an inspection camera? Sounds like I'm missing out on some reveloutionary technology here :-/
 
Last edited by a moderator:

Reply to Taking money for certification - customer dont wanna pay! in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

hi, asking as a customer not a tradesman Having had a rewire and had some issues with the electrician , namely his working standards and the fact...
Replies
34
Views
6K
Im seeking advice from a job we have done with the most difficult customer of my whole career. We're a family business of 50+ years and take pride...
Replies
81
Views
11K
Having just paid another 10,000 shillings (a nod to telectrix) to my scam provider, I was thinking about a more concerted way of passing this on...
Replies
8
Views
1K
hi guys hope some one on here can help me out in looking to be able to self certify my foreigners. I have my 2330 Nvq lvl3 17th edition 3rd...
Replies
27
Views
3K
DuaneMHunt1976
D
Hi guys, I'm a little confused as to how to go about providing certification for domestic. I always though you HAD to be registered with one of...
Replies
24
Views
13K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top