I've seen TT installations where a fault meant live metalwork - not a fun situation.
Exactly, without any additional RCD protection and say a Ze of 80 ohms you'd have a dead short live/earth current of around 3 amps, wouldn't worry even a 6a MCB so all the earthed metalwork sits at mains voltage. :)
 
yeah true but the lucky man here got earth leakage circuit breakers, but its kind of disappointing to see that as all the pipes are connected with the earth and under a fault condition not all current flows to the elcb as some goes to the other pipes and most luckily they have lower impedance compared to the breaker.
Without any intention of causing offence I believe that you have a very poor knowledge of requirements for protection against shock and I strongly advise you to get an Electrician in for safety's sake.
 
Without any intention of causing offence I believe that you have a very poor knowledge of requirements for protection against shock and I strongly advise you to get an Electrician in for safety's sake.+

Without any intention of causing offence I believe that you have a very poor knowledge of requirements for protection against shock and I strongly advise you to get an Electrician in for safety's sake.
Well i do both part time dentist and electrician
 

Reply to TT earthing enquiry. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi How do i access the earth rod to service it, where abouts will it be located and does a tt system have upfront rcds which will be probably in...
Replies
3
Views
990
Carrying out a EICR in a commercial setting. In the main intake room the DNO supply comes in and it states clearly this is a PME system. 5 years...
Replies
5
Views
1K
Keeping this brief.....................New dwelling.....TT system with 100mA S type rcd protected supply to local board with 30mA RCD. Freelance...
Replies
21
Views
3K
On a TT system the rcd must operate withing 0.2 seconds for many circuits. Why when we test rcd's does it not say 300ms for TN systems or 200 ms...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock