Discuss Two 16amp oven installation in the DIY Electrical Advice area at ElectriciansForums.net

D

Deleted member 149081

Hi,

I've searched these forums and have found quite a bit of good information, but not specifically to my query.

My house is about 9 years old. The kitchen has a dedicated cooker circuit, which has a 32 amp MCB.

The cooker circuit only has two single 13 amp sockets on it, and each of these has a single oven connected to it with a 13 amp plug. I'm 99% sure there is not an isolating switch on the circuit (all other appliances do have isolating switches).

I'd like to replace the two 13 amp ovens with two 16 amp ovens.

Am I correct in that in order to do this, I, or an electrician, would replace the two 13amp sockets with, for example, two 20amp DP switches (such as MK K5403WHI) with a flex outlet in the base, and then wire each 16 amp oven into each socket?

Then, because there is no fuse between each oven and the DP switch, it would best to replace the 32amp MCB with a 16 amp MCB so that the entire circuit is rated at 16 amp?

Many thanks in advance for any help.

Tim
 
I suspect if you read the manufacturers instructions they'll tell you to run them on their own circuit on a 16A circuit breaker.

If the 32A circuit is good, I might be inclined to install a small consumer unit in a cupboard and use that to supply two 16A circuits, one for each oven. Make it accessible so the main switch can be used as a DP isolator for emergencies.
 
@Petej999 , is your disagree a mis-click or a genuine disagreement? I only ask because I'm curious about what others might suggest... everyday's a school day and all that :)
 

Reply to Two 16amp oven installation in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi, I have lifetime experience (50+ years) in United States with basic knowledge of split phase 120/240 volts replacing wall switches and...
Replies
5
Views
472
Hi, I'm installing a Hoover oven and would like a little help please. The oven code is HOC3158IN. The oven manual states "The power cable must...
Replies
9
Views
651
Hi all We are hoping to upgrade our oven. We currently have a single integrated oven and a separate induction hob. Each has its own red switch...
Replies
0
Views
838
Hi all, I'm about to replace our kitchen and one of the upgrades is to install two full size ovens to replace the original twin over under...
Replies
7
Views
1K
Hello hope you can help I have a single oven 2.4kw max and a ceramic hob 6kw max I would like to put then both on the same circuit so i was...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock