Agent contacts me with an urgent request for a CU upgrade in Camden. They send over an EICR done the previous month and I have a quick skim. All seems pretty simple, CU needs an upgrade and some basic tidying of fixtures etc. Only 3 circuits so I'm not overly bothered about doing another EICR prior to doing the CU replacement.

Turn up to the property and within 10 mins I note there is no visible MET, nor is there any visible earth supply coming from the head. So I head inside and run some tests, again no earth. So I knock on the basement property and ask to test their installation, again no earth. Ok, so by this point I'm baffled by the lack of a main earth. So I called UKPN who send an engineer and he confirmed my fears, the property has never had an earth supply nor will they add one. As a result, he then issues all 4 flats with a Sec 26 ESQCR notice and turns off power to the entire building.

As you can imagine with 4 privately rented flats each with their own agents and landlords it kicks off. Turns out 2 of the 4 flats had EICRs completed within the past 3 months. One had a new CU installed. The property HAS NO EARTH!

Both EICRs were issued by NICEIC approved installers. Readings were recorded that could not have physically been taken. What is going on!?
 
I’m asking a similar question about no earth into a block of 6 flats
I have attached an email from 3 years ago
Any advice please
 

Attachments

  • 2CF931CB-07B7-4093-9F06-D54663D69B8C.png
    500.5 KB · Views: 30
I’m asking a similar question about no earth into a block of 6 flats
I have attached an email from 3 years ago
Any advice please
Did you get the EICR in the end? If so, what did it say for the type of supply? (TN-C-S, TN-S or TT)?

If they were purpose built flats then a suitable earth should have been provided (and it's possible there is foundation earthing or similar in place). Do you know when they were built?

The main issue of concern with your reading would be to ensure that it is a suitable earth rod or equivalent and not provided via copper water piping or similar. That should have been checked at the time of an EICR, though it can be difficult if there is common piping.

Even if the DNO couldn't provide a PME supply at the time, they may be able to now - though it can get complicated with flats as sometimes the building management has responsibility for internal stuff and not the DNO.

If you don't already, you will want to be checking your RCDs work by pressing the test button very 6 months to ensure they are still in working order.

If you can provide a picture of your consumer unit and your main fuse head/meter, it may be clearer, depending on how things are wired....
 
Did you get the EICR in the end? If so, what did it say for the type of supply? (TN-C-S, TN-S or TT)?

If they were purpose built flats then a suitable earth should have been provided (and it's possible there is foundation earthing or similar in place). Do you know when they were built?

The main issue of concern with your reading would be to ensure that it is a suitable earth rod or equivalent and not provided via copper water piping or similar. That should have been checked at the time of an EICR, though it can be difficult if there is common piping.

Even if the DNO couldn't provide a PME supply at the time, they may be able to now - though it can get complicated with flats as sometimes the building management has responsibility for internal stuff and not the DNO.

If you don't already, you will want to be checking your RCDs work by pressing the test button very 6 months to ensure they are still in working order.

If you can provide a picture of your consumer unit and your main fuse head/meter, it may be clearer, depending on how things are wired....
Hi
TN-S built 1960
The flat is rented out and is good condition all the proper lamps in the bathroom
I will check the RCD tomorrow
It said earth onto copper pipes
 
Hi
TN-S built 1960
The flat is rented out and is good condition all the proper lamps in the bathroom
I will check the RCD tomorrow
It said earth onto copper pipes
Hi
TN-S built 1960
The flat is rented out and is good condition all the proper lamps in the bathroom
I will check the RCD tomorrow
It said earth onto copper pipes
I did get the EICR
 
I have just been told by UKPN to get a TT system
As a new connection would be so expensive


But now seriously
I thought that it was common for letting agents etc to only accept approved contractor status eicr, so do domestic installers just print their own or nip down to tool station.
 
Last edited by a moderator:
But now seriously
I thought that it was common for letting agents etc to only accept approved contractor status eicr, so do domestic installers just print their own or nip down to tool station.
And a lot of those aren't worth the paper they are written / printed on
How does anyone lower their standards to get into these schemes
 
But now seriously
I thought that it was common for letting agents etc to only accept approved contractor status eicr, so do domestic installers just print their own or nip down to tool station.
It may be common but, let's face it AC, DI or cheapo down the pub, when talking EICR the most important word involved is COMPETENT (whether they are or not).
Are NIC insisting on AC's or not? Either way, it's not a legality.

I've been on about it for two decades, on here for the last one.
Started with PAT, on to domestic, then commercial and even industrial.
We see, in life and on this forum, an idea of just how rife is the rot. ....totally letting down and devaluing genuinely competent tradesmen.
It's a total disgrace from top to bottom....Part Pee stinks.
 
Last edited:
It does. A great deal of my early NICEIC work was contracting for local authorities.
Regular C of W was the rule. Now it's leave 'em to it. I watched it get worse in the 2000's when blokes supposedly in charge were coming to me for advice.

When I was a teenager, 'budget cutting' was a short back and sides.
 
Last edited:
COW now that brings back memories, as does RE and RA on larger projects. (anyone remember what they where?)

If the local authorities insisted on a Qualification from a certifying body, this could all change, but the body would need legislating and assent by the Secretary of State to make it viable and not some fly by night organisation made up over a beer mat by a couple of blokes cashing in on the possible legislation.

Now lets think of a name for the body, suggestions on a postcard please.
 
I don't think its a failure of the system, nor the bodies employed for the system, its more to do with the honesty of the individuals carrying out work.

I would argue that the vast percentage of members on this forum are honest individuals, who would only ever carry out accurate reliable works. Are they representative of all electricians, I doubt it.

Honesty has a sliding scale though. If one found a wallet in the street, filled with credit cards & cash. I would like to think most, would take steps to return the item to the owner. If one found a £20 note under an ATM, would you hand it into the bank.
 
If one found a £20 note under an ATM, would you hand it into the bank.
At the rate banks are closing branches it might be difficult to hand it in

A few years ago I found a £10 note on the floor in one of the aisles of a supermarket I handed it in to the customer service desk who seemed totally disinterested, I often wonder was it reclaimed or just went in someones pocket
 
If one found a wallet in the street, filled with credit cards & cash. I would like to think most, would take steps to return the item to the owner. If one found a £20 note under an ATM, would you hand it into the bank.
The former is very easy to prove who the rightful owner is. The latter, nearly impossible. May as well go in your own pocket rather than the bank's
 
Registered is the key word, of course.

Maybe these days it's just stick to R Electrician.
It always has been R Archangel........coz only god can 'lay a finger' on the architect.
Resident is the key word for Resident Engineer and Resident Architect they where the people on site to ensure the building was constructed in accordance with the design, in the day's of the RE and RA it was a requirement of becoming qualified to have spent at least six months on a project to learn the practical building methods, not just the design carried out in the office, this unfortunately does not happen anymore and I think construction is worse off for it.
 
And a lot of those aren't worth the paper they are written / printed on
How does anyone lower their standards to get into these schemes

The former is very easy to prove who the rightful owner is. The latter, nearly impossible. May as well go in your own pocket rather than the bank's
The legal way to do it would be to hand it in to a police station, then if it's not claimed within 28 days then it's yours.
What would I do? , would depend on the time of day, costa, or Burger King :)
 
The legal way to do it would be to hand it in to a police station, then if it's not claimed within 28 days then it's yours.
What would I do? , would depend on the time of day, costa, or Burger King :)
Why would you hand it in to Costa or Burger King?
And what's the time of day got to do with the price of cornflakes? Is it because the police station is closed?
 
Why would you hand it in to Costa or Burger King?
And what's the time of day got to do with the price of cornflakes? Is it because the police station is closed?
I wouldn't eat a Burger King in the morning, but I do like a costa coffee, and neither of them are free.
 
Why would you hand it in to Costa or Burger King?
And what's the time of day got to do with the price of cornflakes? Is it because the police station is closed?
Cop shop? 5 miles to my nearest....used to be 500 yards.
They're cost cut shutting everywhere.............except Costa, Burger King, etc..of course.
Local bank's an ATM now.
 
Last edited:
I don't think its a failure of the system, nor the bodies employed for the system, its more to do with the honesty of the individuals carrying out work.
I disagree.
While the primary cause is lying scum - the thing that lets them get away with it is the failure of the scams to police standards. When registered contractors can do substandard work or miss blatant faults when inspecting, and the scams do nothing about it, then there's precious little holding up standards across the industry. It will be interesting to see what happens with the two involved in missing the lack of earthing and lying about what testing/inspection they've done - my money is "nothing at all" :rolleyes:
 
Cop shop? 5 miles to my nearest....used to be 500 yards.
They're cost cut shutting everywhere.............except Costa, Burger King, etc..of course.
Local bank's an ATM now.
At the local police station by me they closed the custody suite and now take anyone arrested to another police station about 15 miles away the PCC say it saves just around £630k per year somebody has recently costed all the police time lost in tranporting them to another police station when they could be policing the local area and local officers traveling to interview them and it is believed to be costing somewhere in the region of £1.3m people are trying to understand where the saving is
 
At the local police station by me they closed the custody suite and now take anyone arrested to another police station about 15 miles away the PCC say it saves just around £630k per year somebody has recently costed all the police time lost in tranporting them to another police station when they could be policing the local area and local officers traveling to interview them and it is believed to be costing somewhere in the region of £1.3m people are trying to understand where the saving is
Crazy! They probably save by paying less work persons and renting out or selling off prime land properties.
Rubbish, short term budgeting, probably.
 

Reply to Two NICEIC installers failed to spot the lack of earth in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock