Currently reading:
Underfloor conduit for kitchen island unit?

Discuss Underfloor conduit for kitchen island unit? in the UK Electrical Forum area at ElectriciansForums.net

FatAlan

-
Trainee
Esteemed
Supporter
Reaction score
1,827
Any recognised / best practice methods / conduit types for routing cables under floor. I’m looking to feed an island kitchen unit so will be looking to supply an induction hob and sockets.
Will be a completely new floor with insulation on top of concrete, underfloor heating pipes, screed with stone tiles on top.
 
Stick 25mm2 galv conduits in and put a draw wire in, however if the supply to the hob needs to be more than 6mm you will have to think again, PS, make sure the conduit is in one piece without any couplers and make sure any bends flow and are not tight.
 
As MDJ has suggested, last one I did I ran the 20mm2 conduit from a 100mm galvanised box so I could connect T&E to singles and also earth the containment. The other end went straight to a double socket but again a galv box could be used.
 
As MDJ has suggested, last one I did I ran the 20mm2 conduit from a 100mm galvanised box so I could connect T&E to singles and also earth the containment. The other end went straight to a double socket but again a galv box could be used.
Presumably singles are easier to route through the conduit than T&E?
 
With regards to the whole situation im assuming its to be run in conduit for protection against physical damage, thermal damage etc? And also how come it has to be under the ufh?
Cheers guys

How else would you install the cables?

Apart from the ufh unnecessarily warming up the cables, the conduit etc might effect the heating screed/slab and possibly weaken it. You should check with the manufacturer, if you intend to do so.
 

Reply to Underfloor conduit for kitchen island unit? in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock