In a simplistic view, then yes.

If you want the more technical answer, the VA is purely a product of the Voltage produced by the supply and the current drawn from the supply.

Watts is a product of the voltage dropped accross the resistive element of the load and the current drawn from the supply.

Volts Amps Reactive (VAR) is a product of the voltage dropped accross the reactive elements of the load and the current drawn from the supply.


the difference between these values is the Power Factor (ie Watts / VA)

With a power factor of 1, with a purely resistive load (although in practice all loads have some reactive elements) then Watts would equal VA. A generator rated at 10KVa would supply 8Kw at a power factor of 0.8., and 10Kw at unity power factor

VA is quite often refered to as "apparent power", Watts are "true power" and VAR is "reactive power"

All off the top of my head, but I hope this helps!
 

Reply to watts and VA in the Canada area at ElectriciansForums.net

Similar Threads

I have halogen lights in my kitchen under the wall units, there are ten lights altogether bulbs are either 10 watt or 20 watt G4 bulbs ( not sure...
Replies
1
Views
733
I have a lighting circuit cable (1mm) powering a telescope (12 volts) in an observatory total draw 84 watts drawn from a transformer. There is a 6...
Replies
4
Views
291
I am lighting my workshop with LED's. I had all 13W (1500 lumens) but wanted more light on the benches, so ordered some 23W, which is supposed to...
Replies
12
Views
2K
Hi All, We have an old Country villa in Spain. The housing electrics were not good so the house recently has been completely re-wired to a good...
Replies
2
Views
711
I have 3 pendant light fixtures with a total of 540 watts of incandescent bulbs connected to a GE electronic dimmer. The bulbs flutter from bright...
Replies
6
Views
840

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock