Just been along to see a potential client. They want an estimate to upgrade the fuse in their 1 way splittersplitter. It is currently a 30amp cartridge fuse.

They just had a bathroom company redo the bathroom, and they changed the shower to a new 9.8kw unit - which their electrician installed.

I had a look at it and the supply cable which disappears under the floor at the old fuseboard only reappears in a cord pull isolator in the bathroom - maybe 5m away. the problem I have is that the load cable from the splitter is obviously 6mm T&E.

so, I = p/v 9800/230 = 42.61a

Table 4D5 allows for 47amps - clipped direct - but this cable has a way to go and I'd say that at least a third of the run is sunk in plaster and a good bit of that in a new tiling job. So replacing the supply will be messy at best - as well as expensive, and the job has just been done. I can't believe the spark would have let it run through a 30amp cartridge fuse in any case.

I know there should be some allowance given for a short load duration - but what are your thoughts?
 
cable sunk in plaster etc. is still method C. it's only insulated walls that require derating. personally, i'd connect up and clamp meter the cable. bet you can't get it to read more than 38A.
 
Yeah. My first thoughts were to just upgrade the cartridge fuse and splitter to and RCD and CB and suggest changing the shower. I'll check again to see if there is any wall insulation, but I think it probably runs under the floor to the bathroom and then up the wall to the isolator before dropping back down at the other side of the bathroom behind the tiling.
 
Just been along to see a potential client. They want an estimate to upgrade the fuse in their 1 way splittersplitter. It is currently a 30amp cartridge fuse.

They just had a bathroom company redo the bathroom, and they changed the shower to a new 9.8kw unit - which their electrician installed.

I had a look at it and the supply cable which disappears under the floor at the old fuseboard only reappears in a cord pull isolator in the bathroom - maybe 5m away. the problem I have is that the load cable from the splitter is obviously 6mm T&E.

so, I = p/v 9800/230 = 42.61a

Table 4D5 allows for 47amps - clipped direct - but this cable has a way to go and I'd say that at least a third of the run is sunk in plaster and a good bit of that in a new tiling job. So replacing the supply will be messy at best - as well as expensive, and the job has just been done. I can't believe the spark would have let it run through a 30amp cartridge fuse in any case.

I know there should be some allowance given for a short load duration - but what are your thoughts?

You cannot rely on the time curve of the OCPD to effectively draw more current than the rating of the device just because you don't have the load on long enough to make it trip.

Calculate the CCC of the cable with its installation method if this is still over the load demand then fit a 50amp mcb and ensure your Zs value still comply ... this would meet regulations although im only suggestion this method as your situation would need a rewire otherwise i normally wouldn't recommend Omitting O/L protection in domestic.
 
Be even less (around 40/41A) if you use the Real nominal voltage instead of the make believe one!! lol!! Also as Tel has implied above, these shower's stated ratings, are often not actually what you get!!

May be having a blond moment here but doesn't this depend on how the manufacturer calculates the advertised kW? I mean from which level of voltage?
 
Last edited by a moderator:
Nope, they will generally just state the highest KW rating on the box. You might see something relating to voltage related KW ratings in the spec/data but i wouldn't hold my breath.... lol!!

To be honest, i can't really see the point to showers over 8 KW /8.5 KW...
 
Having swapped an 8.5KW for an 11KW in my own bathroom......nor can I! No appreciable difference at all.

pointless. anyway. showers are pants. how the hell can you keep your scotch in one hand and a smoke in the other. give me a jacuzzi bath any day.
 
pointless. anyway. showers are pants. how the hell can you keep your scotch in one hand and a smoke in the other. give me a jacuzzi bath any day.

Indeed. It only happened because the old one was shagged and I spotted a good deal on the bigger one. I'm a fan of the big long soak, too.
 
pointless. anyway. showers are pants. how the hell can you keep your scotch in one hand and a smoke in the other. give me a jacuzzi bath any day.
Surely you would shower first,then get in the jacuzzi,Tel. Or,you would be "swirling around in a cesspit of your own making..." A bar of Wrights coal tar if you identify that reference...:frown2:
 

Reply to What a shower in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top