Where do people record the Ze & PFC of a 3 phase installation, if there is say 10m of 25mm tails between the 4 pole isolator (next to the meter) and the 3 phase distribution board, therefore some (though negligible) resistance?

Do you tend to test at the origin, and record that result, or do you regard the MET as being at the DB (as an extension of what is at the meter position) and do your tests there?

Or both, but only use the one at the origin as a reference, and not record it?

Interested to see what people make of this!
 
I'd say ideally it should be recorded right at the origin of the supply in the building as there's a separate part on Schedules of test results for 'zDB'.
But if there isn't a main isolator at the intake it wouldn't be practical with no access to line conductors without removing a DNO fuse...
On an installation where the DNO fuse, meter and CU are right next to each other I'll generally just do the Ze at the CU main switch incoming terminals, with all main bonding conductors disconnected.
 
I always do it at the bottom of the main switch of the DB, technically that's where the "installation" starts, as any other DB would require another cert. Record the highest reading achieved out of 3 phases (should be the same or very close to each other, same as the PFC).
 
If it's not convenient to switch off the supply so you can disconnect the earthing conductor in order to measure the Ze at the origin, then you cannot measure the Ze at all. You can determine the declared Ze from the DNO, and you can measure the Zs at the DB.
 
If it's not convenient to switch off the supply so you can disconnect the earthing conductor in order to measure the Ze at the origin, then you cannot measure the Ze at all. You can determine the declared Ze from the DNO, and you can measure the Zs at the DB.
Quite a common practice, especially in the office blocks where one of the breakers i marked up "server room" 👍
 

Reply to Where to measure Ze, opinions welcome! in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi - just after thoughts on this please. I've been doing some testing on a 20 year old MCC. On the original EIC, Ze was reported as 0.04 R, PFC...
Replies
18
Views
2K
Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
598
I am trying to understand 3 phase volt drop. I understand single phase VD. Lets say we have a 70 meter run of 35mm, 5 core cable from the supply...
Replies
6
Views
2K
When I joined this forum a decade or so back, there was a discussion going on about a welder that was connected with a 3-core cable to L1, L2 and...
Replies
3
Views
2K
Hi all, My question relates to the omission of overcurrent protection (specifically overload and fault protection) at the origin of an...
Replies
6
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock