Wiring new light advice please

Discuss Wiring new light advice please in the Lighting Forum area at ElectriciansForums.net

Reaction score
0
Hello

I am about to put a new ceiling plate up, its a 3 spot light: https://www.amazon.co.uk/gp/product/B000OS94XM/ref=oh_aui_detailpage_o00_s00?ie=UTF8&psc=1

As per instructions it says it needs an earth. Having taken the old light down, it only used neutral and live. There is however other live and neutral wires going into a little connection block. I have never wired up a light that required earthed before.

Could anyone advise on how I correctly wire up the new light please?

Thanks

Adam

p.s. please see pics

https://i.Upload the image directly to the thread.com/oPEmbZx.png

new fitting:

https://i.Upload the image directly to the thread.com/5S6O8P5.jpg
 
The middle terminal on your new fitting is earth so you need a connection from here to the green/yellow wires (earth). Your two unconnected blues go to N and the unconnected brown to L.
 
Last edited:

Reply to Wiring new light advice please in the Lighting Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock