no hot water.. getting live on white when isolated? Valve not letting heat into tank side of valve.. although messy other wiring seems fine.faulty mid position valve right?
Discuss Y plan fault......................... in the Central Heating Systems area at ElectriciansForums.net
The valve should give priority to hot water so that side should be open sounds like the valve has stuck and is back feeding to the white
no hot water.. getting live on white when isolated? Valve not letting heat into tank side of valve.. although messy other wiring seems fine.faulty mid position valve right?
A Y plan uses a mid position valve, this gives a 60:40 split between DHW and CH when both have demand not DHW priority, a system using a diverter valve would give DHW priority.
Where would the valve back-feed from to cause these symptoms?
Have you confirmed that the programmer and cylinder stat are switching correctly?
If anything is live when it is isolated then it surely is not actually isolated? Do you mean you have switched off the isolator and the white is still live?
Sorry wrong terminology,When there is no power to the valve it should still be open to the hot water side. If there is power on the white when it is disconnected this could be coming from the grey back through the switch in the valve.