Discuss Y plan fault......................... in the Central Heating Systems area at ElectriciansForums.net

bigspark17

-
Arms
Reaction score
718
no hot water.. getting live on white when isolated? Valve not letting heat into tank side of valve.. although messy other wiring seems fine.faulty mid position valve right?
 
If anything is live when it is isolated then it surely is not actually isolated? Do you mean you have switched off the isolator and the white is still live?
 
The valve should give priority to hot water so that side should be open sounds like the valve has stuck and is back feeding to the white

A Y plan uses a mid position valve, this gives a 60:40 split between DHW and CH when both have demand not DHW priority, a system using a diverter valve would give DHW priority.

Where would the valve back-feed from to cause these symptoms?
 
A Y plan uses a mid position valve, this gives a 60:40 split between DHW and CH when both have demand not DHW priority, a system using a diverter valve would give DHW priority.

Where would the valve back-feed from to cause these symptoms?

Sorry wrong terminology,When there is no power to the valve it should still be open to the hot water side. If there is power on the white when it is disconnected this could be coming from the grey back through the switch in the valve.
 
If anything is live when it is isolated then it surely is not actually isolated? Do you mean you have switched off the isolator and the white is still live?

The white wire was disconnected from the wiring centre while testing as i wanted to rule out backfeed. Seems like there is a problem within the switch,no power to either white ot grey should result in valve opening for DHW only.
 
Sorry wrong terminology,When there is no power to the valve it should still be open to the hot water side. If there is power on the white when it is disconnected this could be coming from the grey back through the switch in the valve.

Surely for the grey to become connected to the white, the valve to be stuck at CH only and the white to be live when there is DHW demand microswitch 2 must be stuck on and microswitch one completely shorted between all three terminals?
 
Don’t deal with y plan systems often but Honeywell do 2 port valve with a white wire that is normally closed. Is it possible someone’s fitted the wrong head and your not being given all the information
 

Reply to Y plan fault......................... in the Central Heating Systems area at ElectriciansForums.net

Similar Threads

I had to wire in an extra 2 port valve today to protect a newly installed unvented cylinder (replacing the old gravity fed one) in a standard Y...
Replies
12
Views
2K
I've always thought I was quite good a wiring heating systems, I can do Y plan, S plan, UFH set ups, "normal" thermal stores etc, you name it and...
Replies
4
Views
952
Hello, I hope you are well, I have fitted a few Nests but only to Combi, S and Y plan systems just been looking a job where I’m doing the kitchen...
Replies
9
Views
2K
I have a fully pumped Y plan heating system using a Potterton EP2 programmer. Drayton MA1 Diverter valve. I have just replaced the Actuator head...
Replies
4
Views
620
Hello I have a central heating system, with a Y plan layout. The neon indicator on the thermostat seems to be sometimes dimly lit / flickering...
Replies
1
Views
773

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock