I was reading a Napit factsheet today regarding Ze readings and on it is a diagram showing the earth disconnected from the MET with the earth lead from the tester attached to it with a croc clip, and the L and N leads/probes on the L and N terminals on the incoming supply. Isn't that testing all three wires to the supply?
I tested mine as shown and got a reading of 0.18ohms. Seems adequate enough to me.
 
Have you seen the date on the thread you have posted on?

Your Ze sounds fine even if it was to be a TNCS earthing arrangement.

By removing the Main Earth and testing like you explain you are indeed testing the External Earth Fault Loop Impedance (Ze ---- e = external;))

Please remember that this is a LIVE test and if you are unsure of the procedure and how to perform the test correctly and what you should be expecting to see on your meter then you should be supervised whilst doing so.

Practicing is all good, killing yourself is not so good... Although considering some of the recent threads some opinions may differ lol (Just kidding :))

:thumbsup
 
Have I missed something ? Old thread or not, Ze is taken between between Line and the distributors Earth which is disconnected from the board/MET with the CU isolated.
The OP seems to be describing the tests PSSC and PEFC the greater value obtained being the PFC
J
 
Have I missed something ? Old thread or not, Ze is taken between between Line and the distributors Earth which is disconnected from the board/MET with the CU isolated.
The OP seems to be describing the tests PSSC and PEFC the greater value obtained being the PFC
J

To be fair, he's included the EFLI value at 0.46 Ohms, he just doesn't have a clue what it means or what the recommended upper limits are.
Neither BS7671 nor ESQCR regulations make a maximum limit on Ze values but there was an 'engineering agreement' to attempt where possible to use the commonly known upper limits (0.35 etc etc).
 
I was reading a Napit factsheet today regarding Ze readings and on it is a diagram showing the earth disconnected from the MET with the earth lead from the tester attached to it with a croc clip, and the L and N leads/probes on the L and N terminals on the incoming supply. Isn't that testing all three wires to the supply?
I tested mine as shown and got a reading of 0.18ohms. Seems adequate enough to me.

This is the part I was referring too which is discussing Ze ;)

I think a forum search would have brought up a more recent thread to add to:thumbsup
 
To be fair, he's included the EFLI value at 0.46 Ohms, he just doesn't have a clue what it means or what the recommended upper limits are.
Neither BS7671 nor ESQCR regulations make a maximum limit on Ze values but there was an 'engineering agreement' to attempt where possible to use the commonly known upper limits (0.35 etc etc).

Nor do I please explain ! ha ha
J
 

Reply to Ze reading in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
Hi , Could someone answer the following for me? i don't have reg book handy and when i google i'm getting mixed answers. 1. maximum...
Replies
2
Views
448
OLDBOY
O
On an EICR I found a 200 amp 3ph supply, TNS earthing (which looks original) and Ze of 19 ohms. No rods. No RCDs. L1 -> N was about 0.5 ohms...
Replies
11
Views
1K
Evening everyone . I was changing a fuse board today . Everything tested out fine and good . Until I measured the Ze which is on a tnc-s system...
Replies
7
Views
929
Went to a house to extend a circuit and upon doing the minor works I couldn't figure the earthing system. There was no DNO cutout and L and N came...
Replies
1
Views
761

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock