Anybody know where that post wentt that showed you the acceptable zs values for each protective device? Thought it was a sticky but can't seem to find it anywhere. And before anybody says get a regs book I'm waiting for it to be delivered!
 
Anybody know where that post wentt that showed you the acceptable zs values for each protective device? Thought it was a sticky but can't seem to find it anywhere. And before anybody says get a regs book I'm waiting for it to be delivered!


dont forget good old Ohms Law for the 60898 cb`s which are are going to be the most common device used, its very handy when the reg book is not at hand

type b 5 x In
type c 10 x In
type d 20 x in

for all disconnection times from 0.1 to 5 secs

eg 32A type B x 5 = 160
230/160 = 1.44 agrees with regs as cold value x .80 = 1.15 ohms max Zs
 

Reply to Zs values... in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

So I’m doing my level 3 design project at the moment, and I’m on the question where you do all the calculations on each circuit, I’ve taken the...
Replies
3
Views
1K
Hi All, I'm new to Amtech/Trimble and I've been asked to review a model. I'm looking at circuits that are SWA cables using the armour and an...
Replies
4
Views
524
I’m probably going to look stupid here, but it will be worth it if I get the answer 😆, as I can’t fathom it out. I’ve never really thought of it...
Replies
22
Views
717
Hi All, We have a Merlin Gerin Compact NS100N Single Phase MCCB I've been asked to find its Max ZS Values and to be honest I cant find anything...
Replies
6
Views
3K
Anyone come across this before? I was asked to do a Zs on a 3ph surge device; L1 was around 6 ohm, L2 & L3 around 0.11. Wired in singles from a...
Replies
1
Views
431

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock