One or the other...manual changeover.Are both A & B supplies used at the same time or is it a duty / standby situation?
Thank you...For the Neutral Earth loop on the installation you describe the 0.03Ω sounds about right (as Wilko has just said!)
So the A installation sounds correct but the B does not.
View attachment 39394
Therefore the neutral of the non operational supply (B) is probably not connected to your live supply as this would mix the two systems of the supply transformers.One or the other...manual changeover.
Thank you...
Both supplies are operational..voltage to earth is 240 on both systems..There is some info about earthing neutrals through impedences(fig 44.1)and section 442 .not too clear to me..Therefore the neutral of the non operational supply (B) is probably not connected to your live supply as this would mix the two systems of the supply transformers.
Hi.I cant really comment.I will need to investigate further.The complex has 5 sets of HV/LV Transformer rooms(Subs) (Times 2 :A+B) I believe there are two independant 11,000volt ring mains.They wont let us doe_heads in to the substations.Hi,what is the set-up,regarding the two supply transformers,and what is feeding them?
Ok thanks..Substations arn't really my game.,but I'll try and get more infoHi,it may be beneficial,to find the spec on the supply characteristics,which should be available to yourself.
Maybe not in this case,but some installations can have dual intakes,TN-S and PME,and there are very specific requirements,regarding separation distances,bonding,removable links,etc.