TNS

Discuss TNS in the Commercial Electrical Advice area at ElectriciansForums.net

Therefore the neutral of the non operational supply (B) is probably not connected to your live supply as this would mix the two systems of the supply transformers.
Both supplies are operational..voltage to earth is 240 on both systems..There is some info about earthing neutrals through impedences(fig 44.1)and section 442 .not too clear to me..
Incidently when I measure on megohm scale I am showing 0.00
 
Hi,what is the set-up,regarding the two supply transformers,and what is feeding them?
Hi.I cant really comment.I will need to investigate further.The complex has 5 sets of HV/LV Transformer rooms(Subs) (Times 2 :A+B) I believe there are two independant 11,000volt ring mains.They wont let us doe_heads in to the substations.
So I could still be looking at either a neutral earth fault or a missing earth link on neutral...I've been trying to read up but it appears the HV earth &LV earthed neutral can either be separate or common or through an impedence..
 
Hi,it may be beneficial,to find the spec on the supply characteristics,which should be available to yourself.

Maybe not in this case,but some installations can have dual intakes,TN-S and PME,and there are very specific requirements,regarding separation distances,bonding,removable links,etc.
 
Hi,it may be beneficial,to find the spec on the supply characteristics,which should be available to yourself.

Maybe not in this case,but some installations can have dual intakes,TN-S and PME,and there are very specific requirements,regarding separation distances,bonding,removable links,etc.
Ok thanks..Substations arn't really my game.,but I'll try and get more info
 

Reply to TNS in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

I would like to get some information on what protection is on a multi meter when accidentally testing a live circuit while the meter is on the...
Replies
1
Views
503
On an EICR I found a 200 amp 3ph supply, TNS earthing (which looks original) and Ze of 19 ohms. No rods. No RCDs. L1 -> N was about 0.5 ohms...
Replies
11
Views
1K
Evening everyone . I was changing a fuse board today . Everything tested out fine and good . Until I measured the Ze which is on a tnc-s system...
Replies
7
Views
920
Hi was recently at a property and was installing a Solar PV system. was doing my testing and i came across a weird result when doing the...
Replies
23
Views
3K
Hello. New member here. Electrical enthusiast. I am at a friend's house in the Bahamas and decided to look at the load center in the house, which...
Replies
2
Views
430

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock