final

  1. S

    Radial final circuits in garage

    Situtation is a new, small garage (16 sq m) fed from the house via a 16A mcb and 30mA main RCD. I am doing my own installation under a Building Notice to the local council building control dept. Plans filed with the application are for a garage unit with 1 x 6A mcb for lighting, and 1 x 16A mcb...
  2. A

    continuity of ring final circuit

    Hi Just doing end to end test line - line 0.51ohms seems fine cpc-cpc 0.91 ohms seems fine But N- N reading is coming up 1.46 Kilo ohms ??!!! any thoughts I am doing 2392-10 and am fairly green.............be gentle angus
  3. S

    Ring Final Circuit advise query

    Hi guys, Would be interested to hear your thoughts on the following. I had to change a CU in a hoarders property in January which proved to be quite a challenge. CU was damaged with accessible live parts so I had no choice. Clutter was extreme with hardly any access to some rooms so couldn't get...
  4. B

    Distribution of load on a ring final for Voltage drop calcs?

    Just pondering my voltage drop calcs for a fused spur off a ring final. Additional circuit will be around 15-20m long so I though I should do this properly.... My problem is calculating the voltage drop in the existing ring to the point of the spur which of course depends on distribution of...
  5. R

    Continuity of ring final circuit conductors

    Why is it when you cross connect the conductors at each leg and then test continuity, the result is one quarter of the combined resistances of the legs? I am usually pretty good at seeing how/why calculations work out, but just cannot in this case get my head around why the value measured is a...
  6. M

    Ring final circuit

    Hi Guys Can someone tell me please what is the difference between a ring main and a ring final circuit.....thanks in advance
  7. Y

    extend ring final

    Hi Chaps I am just starting out in this profession and eager to learn so sorry if questions seem a bit daft. If you need extend a second floor ring main which runs through four rooms by a further two sockets , and you have no idea where the first or last socket is where do you break into the...
  8. F

    No cpc continuity on ring final

    Hi all, Had a call from a customer saying her oven had broken. When the oven engineer went out he fixed the oven but told her she had "no earth on her kitchen sockets".?!?! He told her the other circuits ie the lounge and cooker, were ok but no earth to the kitchen ring final?! How can this be...
  9. N

    LED bulbs Dim glow!!!!

    I went out to a property today and the tenant had 6 down lights connected to a 3 way switch system. The down lights worked great! When the tenant installed LED bulbs there seemed to be a dim glow from the bulbs. The bulbs are 240V 2W. When the switches are off there is 47V at the fittings. Can...
  10. M

    Separation of circuits 314.4

    Hello, I'm doing a periodic inspection and am unsure weather to fault this, I have a generator which is the source of my supply, this then feeds two main distribution panels out of the main switch. So there is two 3 phase supply cables out of one MCCB. Does 314.4 come into play or does it...
  11. Baker1988

    Dangers of ring final circuit

    Hi i have been set some home work from college to find out why ring final circuits are dangerous. I know the obvious that if one leg on the ring breaks it will not be a full ring and the 32 amp mcb will be too big for the cable as it will only be able to carry about 20 amps with out it been a...
  12. E

    Downstairs sockets

    The house I recently purchased has got the downstairs s/o on one circuit. There are 4 in the kitchen and 4 in the lounge. Does the kitchen need to be a seperate circuit? To me it seems daft just having 4 s/o on one circuit.:rolleyes2:
  13. P

    Slightly high Zs on large ring circuit

    Hi all, I did a PIR yesterday at a largeish house (150m2). there is only 1 ring final circuit for all house sockets. Zs was 1.25ohms, vs 1.16 permitted maximum value. there is an RCD so additional protection in theory although the RCD did not disconnect at 5x 30 ma test. I will obviously...
  14. R

    Guidance on installation certificate

    Hi. First post so be gentle. I guess its always the obvious things that slip your mind.. Im adding a new final ring to existing consumer unit.. Does schedule of test results have to include mesurements for all circuits on within the installation or can i just cover the new circuit? Thanks for...
  15. E

    Led glow

    Installed led spotlight on landing controlled by 2 way switch. When switched off it continues to glow. Presumably this is an induced voltage in the strapper. Is there any cure or even any need to cure it?
  16. F

    Domestic extension to Ring Final - Earth Bonding to Services advice

    TN-S Domestic, 30mA RCD, 32A MCB, 2.5mm T&E I've been asked to install some socket outlets and connect up previously installed underfloor electric heating (2400W) plus some wall lights in a Conservatory project that got built, but electrical works not completed by the the time the building firm...
  17. L

    What Reg states you cant have 2 RFC's in one fuse?

    Hey guys, just out of interest, just completed a job for a customer but whilst i was in the board(old 5 way wylex) i noticed both ring circuits on one 32a fuse (space saving?)and cant rememeber off the top of my head and wondered if one of you lovely people knew the actual reg that states its a...

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock