Discuss 10w led floodlight /protection in the UK Electrical Forum area at ElectriciansForums.net

J

joehat

Hi all

Question 1

Is a flood light omitted from over current protection?
I normally go a lighting circuit but this job would be a lot easier if coming from the outside socket, which is part of the ring,
As this is fixed, would it be okay to wire it in 1mm or 1.5mm flex, without over current protection, eg like a spur I guess as this doesn't.

Question 2

Would you be happy feeding a 10w led flood light from a sour socket, as its such a small load?

I would say yes to both but I've had people say no you can't .
 
For example a spur socket is omitted? As in the mcb would be 32a yet the cable could be rated less than 20a in certain install meathods?
 
For example a spur socket is omitted? As in the mcb would be 32a yet the cable could be rated less than 20a in certain install meathods?

If the installed cable was derated to less than 20A on a 32A circuit, even a ring, then the circuit would have not been designed properly.
 
You could fit a weatherproof FCU adjacent to the external socket and connect the light to that using a 3 amp fuse, even a 1 amp would be fine.
 
Isolation requirements for adjustment, general maintenance etc
Reduction in cable size on the ring would require appropriate down fusing over 3m ( Supplying fixed load )
Zs would still need to comply (You have reduced the earth size thus increased the Zs Value against the 32amp mcb/rcbo)

Yes in theory you could wire direct to a 32amp mcb in the board with 1mm cable but as you are asking about tapping onto a ring then you have other regulations to consider here, with the exception of socket circuits, most house circuits can be classed as fixed loads if you know the max' demand possible, we of course don't do this in practice in domestic as its not the done thing and can be very confusing to others who follow so we all tend to design and wire without using the omittance clause.

If the light was within a 3m run of a socket it was tapped off then yes you could argue it is within regulation to do this but just from a maintenance aspect, I would be running it through a suitable Sw/F spur. Also to note, the manufacturers instructions may require fusing down but this is manufacturer dependent.

In my sector this clause comes into its own as I use it regular when allowing larger breakers to counter nuisance tripping due to inrush on fixed load equipment.. this be more the targeted application of this regulation.

Personally in my opinion, you shouldn't be looking to use this clause in domestic like in your example, add a fused spur as is the general practiced method.
 
Last edited:
The spur via a FCU, your max Zs would change as it would be protected by the 1362 fuse in the FCU so the max Zs for the light via a 3A fuse is something like 17ohms
 
What about in 2.5mm flex? Like a double socket spur ?

Customer wants least mess possible, and isn't doing it in 2.5 the same as an infused spur Anyways??
In the osg it states an unfused spur can be one single or double socket or one perminately connected appliance ?
 
Customer wants least mess possible, and isn't doing it in 2.5 the same as an infused spur Anyways??
In the osg it states an unfused spur can be one single or double socket or one perminately connected appliance ?

What's messy about a suitably IP rated FCU close coupled to the outdoor socket ? Has it been confirmed that the outdoor socket is within the RFC properly as it is common practice to spur off for an outdoor socket addition ?
 
Customer wants least mess possible, and isn't doing it in 2.5 the same as an infused spur Anyways??
In the osg it states an unfused spur can be one single or double socket or one perminately connected appliance ?

The customer may want ..... But it's your job to install to th regs. My advice is quote to do it properly or walk away.
 

Reply to 10w led floodlight /protection in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have a baffling problem with a newly-installed PIR floodlight and I'd like advice from the forum as to whether it's defective (and should be...
Replies
5
Views
518
The stately home I work with has asked me to repair a couple floodlights not working. Mounted very high up… I could hang over the roof and checked...
Replies
15
Views
2K
Hey guys, looking for a bit of advise on the installation of an outside light. I plan on chasing out the plasterboard and running a cable from a...
Replies
16
Views
3K
Hi all, I have a single switch in my garage to turn on a couple of lights in there. Yesterday I fitted a floodlight outside, drilled through...
Replies
13
Views
2K
We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
619

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock