I am attempting to help a friend. This is a small commercial building. Someone has pulled a 110v circuit from one leg of a 3 phase panel and it has ceased functioning (I am assuming it worked at one time). I have one of those little plug-in-outlet testers for polarity etc and it shows all is well. Another tester that just shows a light for the appropriate voltage lights the 120v light, but when I check voltage with a vom I get approx 141v and nothing plugged into the outlets works. The hot is connected to a breaker on one leg of the three phase and the neutral goes to what would be the neutral bar in the box. The problem is I do not see a neutral coming into the box, just the three large hot wires for the 3 phase and the neutral bar APPEARS (I have not checked continuity yet) to be connected to the ground bar. About all the info I have at this point. Anyone have any thoughts?
 
I am more familiar with the UK power supply, but from your readings you have voltage at the outlet as expected but nothing will run.It would be a good idea to check if it ever worked and if so if anything has changed in the intervening time.Other than that it sounds like you have a loose connection somewhere, where there is just enough contact to supply a voltage but it breaks down when it draws current to power a load.Check the neutral connection (in the UK at the incoming supply the neutral could well be connected to ground, but there are different arrangements in the US) and also check that the breaker is functioning correctly, it may be just starting to break down and not close properly.
 
You clearly don't know what you're doing. Get a registered electrician to have a look. I will make a site visit for travel expences and accommodation fees.
 
I asked an honest question. No need for the snarky response. The poor connection idea is good. Good enough connection for a meter but not enough to carry any load. Thanks
 

Reply to 110 from 3 phase in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

Absolutely losing my brain here guys What I would like to be able to do is power our 3 phase motor on a single phase supply. Thought I had it...
Replies
3
Views
678
BIG place OK lots of electrical bits. but one on a 3 phase Radial is tripping its RCCB so i check the wiring making sure its tight and it has...
Replies
5
Views
377
Hi everyone, I have been asked to pull in some new 3 phase supplies for 7 new welders which do not require a neutral connection. The client has...
Replies
4
Views
768
Hi all, We have a limited in house PAT testing requirement and were advised that the TIS700 fitted our needs. The unit works fine for 110V and...
Replies
0
Views
712
I know the effect of a lost neutral (floating neutral) on a 3 phase system, and the theory of why the line voltages can vary. However, I have...
Replies
1
Views
786

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock