Discuss 110v earth loop impedance in the UK Electrical Forum area at ElectriciansForums.net

M

matdom

My test meter only works on 230v....

So... Is there a way of working out the Earth fault loop impedance on a 110v supply that is supplied by a hardwired 110v Centre tapped to earth transformer?

Anyone else come across this.

I have some additional 110v sockets to fit in a workshop but need to get this figured out for Minor works cert.

Any help would be appreciated.

Cheers
 
Your going to need to borrow another test meter if you want to measure the Zs. If not you'll have to just calculate it in the same way as normal.

Remember the maximum permitted Zs for MCBs @55v is significantly less than @230V
 
Been looking on the net for info on this and it doesn't appear it's that straight forward, not saying you're wrong obviously.

it's not on MCB it's got 88's in the board.
 
yeah, I know what the MAX is, I just need to find a way to get a reading without a meter, But looking on the net, it seems a bit of an oddball, I found one post that says it doesn't even need testing because technically there isn't a real protective earth as it will constantly sit at 55v anyway???

just a bit stuck with it really!

the only thing I can think of its doing 2 readings, one for supply (Primary side of tran) and then a second for the output side (Secondary winding on transformer)
 
I was just trying to find a bit of clarity on it because the more I thought about it the more I confused myself......but some of the crap written on the net is worrying.
 
Measure R1+R2 at each point of the 110V circuit through each side of the windings, a DEAD TEST that is (just thought I'd throw that in for clarity), and record the highest value. Divide this value by the expected power factor of the 110V system and there's your earth fault loop impedance value. When working out earth fault loop impedance on the secondary side, the primary side doesn't even come into it.
 

Reply to 110v earth loop impedance in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Two related questions in 1, if anyone is up for helping! (i) When electricians install supplies, is there anything in the regs that says how many...
Replies
2
Views
1K
G99 GSI-3 4.4 kw Victron inverter install with EES and batteries and installer can set the export lint if required by dno As part G99 GSI-3 you...
Replies
5
Views
1K
Hi! Some help would be appreciated! I've just moved into new house, wanting to check insulation resestance etc as getting some nuisance...
Replies
2
Views
340
Morning all, Really hoping to get some advice / confirm what a few of us are thinking about a job in the future. Back ground - We have to swap...
Replies
15
Views
449
Hello I’m a student learning about industrial wiring and circuits and we’re about to start learning about how to do loop impedance calculations. I...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock