Discuss 110v power issues in the Commercial Electrical Advice area at ElectriciansForums.net

Reaction score
3
I work on a site that has a transformer which supplies 10 commando sockets at 100v.
Recently, I have been unable to run 110v equipment, such as drills on these sockets.

I have checked the transformer which is 110v from Live to Neutral and 58v Live to Earth; which is correct. I am also getting these readings at each commando socket which doesn't work.

I have tested the same drill on another 110v circuit and it works fine. I have even compared the readings of the sockets on the different circuits and they are the same; give or take a volt or two.

So, I am totally perplexed!! Any ideas ?
 
I wouldn't worry about the L-E voltage. Retest the L-N voltage with some load on one of the 110v sockets. If the voltage is significantly less than your off-load test result then disconnect it and check the continuity of the transformer windings. Maybe also use an analogue voltmeter for the tests.
 
1.bad connection breaking down under load.

2. transformer overloaded and/ or too long cable runs causing volt drop under load.
 
As Tel said,bad connection,check the mcb,s on the front panel it,s possible they may be faulty,dust ingress etc.Quickest solution is to ring the hire company and get them to bring a replacement.
 
Have you checked at the transformer,or just at the secondary distribution point.Normally these transformers are centre tapped to earth L1 to E 55v. L2 to E 55v. L1 to L2. 110v.(check the tally plate) Just think about it and work methodically through the circuit.
 
Just to be pedantic there is no neutral conductor on the secondary side.

I work on a site that has a transformer which supplies 10 commando sockets at 100v.
Recently, I have been unable to run 110v equipment, such as drills on these sockets.

I have checked the transformer which is 110v from Live to Neutral and 58v Live to Earth; which is correct. I am also getting these readings at each commando socket which doesn't work.

I have tested the same drill on another 110v circuit and it works fine. I have even compared the readings of the sockets on the different circuits and they are the same; give or take a volt or two.

So, I am totally perplexed!! Any ideas ?
 
The fact that I've obtained correct readings from commando points just threw me off course slightly. My experience in fault finding on transformers is not great, so this forum has been very helpful. Thanks once again for all your feedback bar one of you, I think you know who you are.
 
The Transformer is quite old, so may need to be replaced.

Transformers don’t wear out. They may burn out.

You need to do the full range of tests on it. As RoB said, it’s basic stuff.

If you are a trainee either RoB or myself will help out. For myself I won’t do training in open forum due to others getting in the way.
 
Transformers don’t wear out. They may burn out.

You need to do the full range of tests on it. As RoB said, it’s basic stuff.

If you are a trainee either RoB or myself will help out. For myself I won’t do training in open forum due to others getting in the way.

Hellooooooooooo Tony!!! :seeya:
 

Reply to 110v power issues in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi all, We have a limited in house PAT testing requirement and were advised that the TIS700 fitted our needs. The unit works fine for 110V and...
Replies
0
Views
698
I have a lighting circuit cable (1mm) powering a telescope (12 volts) in an observatory total draw 84 watts drawn from a transformer. There is a 6...
Replies
4
Views
316
Hi all, New to the forum. I have been asked to look at this for one of our guys who's had an issue onsite after some electrical works had been...
Replies
4
Views
798
Hi everyone, I need help installing a Lorex smart doorbell. I have tried to install a doorbell transformer several times to no avail. The first...
Replies
2
Views
1K
Hello, So I purchased a Novopal 2000w/4000w(Peak) Pure Sine Wave Inverter DC 12V to 110V/120V. I purchased this so I can hook it up directly to...
Replies
5
Views
648

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock