Hi All
I am designing a 110v system for a local workshop. They have speced 20 outlets not all to used at one time. Id think realistacally 40% would be the max.
My question is i have been speked at 15KVA tran with 2 80amp outlets and they say to daisychain 10 sockets from each outlet. They cant quite seem to understand that i ahve to spec my cable to 80amps and are asking me to daisy chain from each 16amp outlet....
I would be under the impression that a dedicated 110v DB would be better with 16amp mcb's for each outlet. Would these want to be d/p mcb's? rated at 16amp?
As you can probably notice i have never done any 110v before. ANy help would be apreciated.
Thanks
Mark