Discuss 115vac line tests with proper voltage, powers a low watt bulb but will not run a drill. in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
I have a 115vac line that tests with proper voltage and will power a low watt bulb but will not run a drill etc...

Line from main panel to barn is 10-3 copper on a 30amp breaker.
Sub panel has two 20amp breakers one for lights and one for plugs.
Wire was run 30 years ago and ran a vacuum sweeper as recently as last fall.
Went to plug in the battery charge for the lawn mower yesterday and nothing.

I connected an outlet directly to the red leg of the sub panel and it will power a hand drill.
But when I connect the same outlet directly to the black leg, it will light a test light but not power a drill.
Both circuits test at 115v.

I pulled the wires off of the main breaker and out of the sub panel and connected the red and black together in the main panel and
they tested for continuity in the barn.
To be sure the 30amp breaker in the main panel was working, I switched the red and black wires and the red still ran the drill and the black did not.

It appears that the amperage is somehow dropping below what the drill needs to operate but powers a test light.

Could the black wire be partially severed somewhere so that voltage makes it through to give a voltage reading and power low watt bulbs but the wire is too thin at the partial cut to push amperage necessary to power the drill? Or, could the wire be completely severed but still touching enough to send voltage but as soon as the drill needs amperage to operate?

There are no staples, nails, insulation cuts etc... through the wire from panel to ground on either end.
The ground has never had anything heavier that a lawn mower go across the buried section.
All the screw lug connections are tight.
There are no moles, wood chucks, etc... anywhere near the area.
There could be rock or something in the ground that took 30 years to wear through the wire, but I'm skeptical.
 
I have a 115vac line that tests with proper voltage and will power a low watt bulb but will not run a drill etc...

Line from main panel to barn is 10-3 copper on a 30amp breaker.
Sub panel has two 20amp breakers one for lights and one for plugs.
Wire was run 30 years ago and ran a vacuum sweeper as recently as last fall.
Went to plug in the battery charge for the lawn mower yesterday and nothing.

I connected an outlet directly to the red leg of the sub panel and it will power a hand drill.
But when I connect the same outlet directly to the black leg, it will light a test light but not power a drill.
Both circuits test at 115v.

I pulled the wires off of the main breaker and out of the sub panel and connected the red and black together in the main panel and
they tested for continuity in the barn.
To be sure the 30amp breaker in the main panel was working, I switched the red and black wires and the red still ran the drill and the black did not.

It appears that the amperage is somehow dropping below what the drill needs to operate but powers a test light.

Could the black wire be partially severed somewhere so that voltage makes it through to give a voltage reading and power low watt bulbs but the wire is too thin at the partial cut to push amperage necessary to power the drill? Or, could the wire be completely severed but still touching enough to send voltage but as soon as the drill needs amperage to operate?

There are no staples, nails, insulation cuts etc... through the wire from panel to ground on either end.
The ground has never had anything heavier that a lawn mower go across the buried section.
All the screw lug connections are tight.
There are no moles, wood chucks, etc... anywhere near the area.
There could be rock or something in the ground that took 30 years to wear through the wire, but I'm skeptical.
Take your receptacle loose and replace. You have a bad connection in the wiring
 
As I said in my post I pulled the wires out of the sub panel and connected directly to a new receptacle. Plus this receptacle works on the red leg.
Then I would say that your buried wire has gotten damaged, probably been like that for years and is just now showing up. Good luck
 

Reply to 115vac line tests with proper voltage, powers a low watt bulb but will not run a drill. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Extremely low voltage on 120v line Hi, I’m not an electrician but my home has 20 amp breaker that has only one outdoor outlet on it with a GFCI...
Replies
2
Views
561
I have a Single Phase Power box for a townhouse. When I read voltage across the Hot legs (A) and (B) to ground I get 123 volts with the main...
Replies
1
Views
937
I thought that I posted this in the DIY part of the forum but I believe I did not. I am sorry about that. I put in a 10' x 20' metal shed about...
Replies
2
Views
1K
Hello, I live in Mexico, where I have a small, un-official trailer park on my property. The property is serviced by my privately owned, 650amp...
Replies
9
Views
1K
I have an existing EmerGen Switch installed in my main panel that links to 10 breakers. The main panel is located in the basement. I recently...
Replies
2
Views
888

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock