Hello all,
I'd like some advice on wiring up a 24V leisure power system. It seems to work so far, but my wiring doesn't seem to match many other diagrams online. I'm worried that I'm damaging batteries or wasting power.
I have 4x 12V Lead Carbon batteries (all identical). I want to have 24V output, and the ability to turn off half the batteries (for whatever reason) and still use the other two.
I have wired up:
2 x 12V batteries in a series bank. The +ve lead heads through an isolator switch to the +ve distribution busbar. The -ve lead heads to the -ve busbar.
and....
another the same.
So, I have two completely independent isolatable 24V banks, joined at the two busbars.
1. Is this right? So many diagrams seem to have leads linking the banks - why?
2. As they are Lead Carbon, will the batteries in series (so, within each pair), balance each other 'naturally' and safely?
3. As they are joined at the busbars, will one 24V bank try and balance with the other if there's a voltage difference? If so is this inefficient or dangerous?
Discharging sounds fairly straight forward.
For charging, this happens when the batteries are offline, and each 12V battery has its own fast charger (mostly due to the cost and size of chargers that will charge 24V @ 50A vs. two that do 12V @ 50A). Is there anything I need to be careful about? I presume I must ensure all are the same voltage before going back online, or will they safely balance if I don't?
4. Is there somewhere sensible to place an active battery balancer? Perhaps to link each bank of 24V together?
Thanks.
I'd like some advice on wiring up a 24V leisure power system. It seems to work so far, but my wiring doesn't seem to match many other diagrams online. I'm worried that I'm damaging batteries or wasting power.
I have 4x 12V Lead Carbon batteries (all identical). I want to have 24V output, and the ability to turn off half the batteries (for whatever reason) and still use the other two.
I have wired up:
2 x 12V batteries in a series bank. The +ve lead heads through an isolator switch to the +ve distribution busbar. The -ve lead heads to the -ve busbar.
and....
another the same.
So, I have two completely independent isolatable 24V banks, joined at the two busbars.
1. Is this right? So many diagrams seem to have leads linking the banks - why?
2. As they are Lead Carbon, will the batteries in series (so, within each pair), balance each other 'naturally' and safely?
3. As they are joined at the busbars, will one 24V bank try and balance with the other if there's a voltage difference? If so is this inefficient or dangerous?
Discharging sounds fairly straight forward.
For charging, this happens when the batteries are offline, and each 12V battery has its own fast charger (mostly due to the cost and size of chargers that will charge 24V @ 50A vs. two that do 12V @ 50A). Is there anything I need to be careful about? I presume I must ensure all are the same voltage before going back online, or will they safely balance if I don't?
4. Is there somewhere sensible to place an active battery balancer? Perhaps to link each bank of 24V together?