739
I'm currently in the middle of gutting the downstairs toilet. It will only have a toilet and a small cloak room sink.

I plan to have a mirror and x1 2 gang socket outlet for the misses to straighten her hair because she refuses to do in the bedroom because there is no mirror.

Is this deemed acceptable? It's not a bathroom or any other special location?

The consumer unit is on the wall behind the toilet so it makes sense to utilise one of the spare ways.

Quick thoughts on a circuit are to install a radial on a 20A mcb. 4mm t+e. Length will be amount 1 metre.

I would like a socket that's as flush as it can be against the tiles. I've seen this which looks good.

GU3220WPW - 2 Gang 13A Switched Double Socket in White Metal Flat Plate White Insert Schneider GU3220WPW - https://www.sparksdirect.co.uk/2-gang-13a-switched-double-socket-in-white-metal-flat-plate-white-insert-schneider-gu3220wpw#.WvWJPNAo9-E

Thanks
 
I'm currently in the middle of gutting the downstairs toilet. It will only have a toilet and a small cloak room sink.

I plan to have a mirror and x1 2 gang socket outlet for the misses to straighten her hair because she refuses to do in the bedroom because there is no mirror.

Is this deemed acceptable? It's not a bathroom or any other special location?

The consumer unit is on the wall behind the toilet so it makes sense to utilise one of the spare ways.

Quick thoughts on a circuit are to install a radial on a 20A mcb. 4mm t+e. Length will be amount 1 metre.

I would like a socket that's as flush as it can be against the tiles. I've seen this which looks good.

GU3220WPW - 2 Gang 13A Switched Double Socket in White Metal Flat Plate White Insert Schneider GU3220WPW - https://www.sparksdirect.co.uk/2-gang-13a-switched-double-socket-in-white-metal-flat-plate-white-insert-schneider-gu3220wpw#.WvWJPNAo9-E

Thanks
Why 4mm2 Gaz?
 
Yes Mate just got back from Tesco, welcome anytime, although there is one member who thinks I drink 3 or 4 bottles at a time.
well that's just plain silly. how can you fit 3 - 4 bottles in your gob? mind you with some members it might be OK.
 
Put the mirror in the bedroom then, not the toilet. Mirrors are not notifiable, nor do you have to do testing.


Yeh I understand that. Other issue is, we have 2 small children. In the morning it's not a good ideal to have to either go upstairs and straighten hair or to have to take the kids upstairs just for that.

It's just easier for us this way
 
.

13730747_1053589748011609_1601688944_o.jpg
 
OP, is the 4mm from your garage correctly colour coded i.e. Blue/Brown? How do you intend to run it from the CU to the socket?

Yep it's harmonised colours. Only purchased about 6 months ago for a A2 radial.

Like I said the C/U is on the other side of the wall. I'll come out of the C/U, into some YT2 trunking and through wall with some conduit.
 
I've always said single or double for a socket, one,two,three,four gang etc for switches. Missed another post writing this so could be 44. :D
 

Reply to 13A socket outley (downstairs toilet) in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
Okay, so, I’m currently working towards becoming an electrician and was after some guidance for a job that I’m working on. The property (a small...
Replies
19
Views
19K
Hi all, I have a frustrating problem: I had planned to add a new double socket in my living room, which has no power cable run/sockets down one...
Replies
1
Views
2K
I have two cables for wall lamps (1mm T+E) going to one of the socket in the back of the TV. These lamps will be controlled with smart bulbs with...
Replies
10
Views
3K
Hi Happy new year to you all. Ive just had a sort out of my stores. Please see below a list of electrical items for sale. Will sell individually...
Replies
4
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock