Hello.

I have a work light, very similar to the one in the picture below. It is a 230v 150w halogen light but the cable is only 2 metres long. If I replace the cable with 2.5 flex, how long can I have it, would realy like it about 20-30 metres, is this ok?

Thanks

p4778536_l.jpg
 
If I replace the cable with 2.5 flex, how long can I have it, would realy like it about 20-30 metres, is this ok?

The IEE Code of Practice for In-service Inspection and Testing of Electrical Equipment suggests a maximum of 25m for a flexible cord of 2.5mm2. However, as another poster points out, it is a bit on the big side for a 13A plug.
 
Use 1.5, it should still be ok, providing you use a 150W lamp. However, like the last post said, max 25M but I think the get out clause with that is that anything over that and it must be RCD protected, but you can get round that by wiring it to one of those plug in RCD jobbies
 
ok, if I use 30 metres of 1.5mm 3 core flex, will this be ok? Providing I use a RCD adaptor?
 
Last edited by a moderator:
1.5mm2 suggested maximum is 15m. As roukel01 has said the get-out clause is if it's supplied by an RCD.
 
You are safer keeping the lead to the light at 2-2.5M because if you plug a 230volt ext lead with an RCD fitted then you can utilise it for other things.

Also if you use it a lot the it may be prudent to change it to a 110 supply just for safety an public liability as "making up" a lead could cause you problems in the future if the flex gets damaged and is not plugged into an RCD supply. I have seen this in the past with home made leads and portible RCDs that highlight a fault but joe builder thinks it is faulty so he takes it out of circuit so now theres a new ball game for you and your insurance company who then ask if the equipment you are using comply with the BS or EU safety standards mark on them and when you say no they leap up in the air do a backflip and then tell you your not covered.

Just a thought..

PS I remember a past 14th or 15th edition that stated that all portable equipment should only have no more than a 2-2.5M lead fitted as the appliance and lead are seen as 2 seperate pieces of equipment
 
I haven't got one long enough! :)

If I bought one for eg, B&Q have a 45 metre one cheap at the min, would that have to be rcd protected because i don't think it has rcd built into it?
 

Reply to 150w work light in the Australia area at ElectriciansForums.net

Similar Threads

Hi. I'm an I.T.. engineer with some outdated electrical experience. I qualified C&G 2330 17th edition about 15 years ago, but my only experience...
Replies
4
Views
791
Hi guys I have some industrial lighting circuits to wire in a workshop and was after some fresh ideas/suggestions as to how i could best do this...
Replies
12
Views
1K
I have halogen lights in my kitchen under the wall units, there are ten lights altogether bulbs are either 10 watt or 20 watt G4 bulbs ( not sure...
Replies
1
Views
739
Looking for a bit of advice from the wider audience / those who may have done similar before. I entered the game a bit later / in a non...
Replies
12
Views
668
Just thought I'd share this quick sobering story that happened to me a couple of weekends ago.... Overhead 230v lighting festoon, LED golf ball...
Replies
5
Views
743

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock