Discuss 16 amp commando sockets. 20 amp mcb on site guide as maximum value mcb in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
19
Hello the on site guide lists 20 amp maximum mcb for 16 amps sockets. Having a debate with someone as to why this is? Why not 16amp mcb? I installed 20 amp mcb as it's for a car charger that charger's at 16amps for 8 hours and is not capable of pulling more than 16 amps but this has been pulled as a C2. I didn't install 16amp as have in the past and over time the bi metallic strip has worn and started to trip after 12 months or so.

Cheers
 
assuming the cable is 2.5mm (or greater) then a 20A MCB is fine to protect the cable. as it's a dedicated load incapable of overloading the 16A socket, then i can't see a problem.
 
Hello the on site guide lists 20 amp maximum mcb for 16 amps sockets. Having a debate with someone as to why this is? Why not 16amp mcb? I installed 20 amp mcb as it's for a car charger that charger's at 16amps for 8 hours and is not capable of pulling more than 16 amps but this has been pulled as a C2. I didn't install 16amp as have in the past and over time the bi metallic strip has worn and started to trip after 12 months or so.

Cheers

Who has coded it a C2 issue ?
Have they quoted a regulation that it does not comply with ?
 
I have gone back with page 184 on IET on site guide 20 amp maximum. It's 2.5mm over 10 meters. I don't know who has gave it a c2 as this is coming from the customer I did the job for 18 months ago.
 
then get the customer to enquire as to the specific regulation that applies to this C2.
 
I wouldn't Code it at all but if a 16A device trips then it is inadequate for the connected load and this must also apply to the 16A socket, change it to a 32A socket.
 
if the charger is designed to plug into a 16A socket, then the 16A socket is sufficient.

going by the argument of whoever coded it, that means we need to fit 13A socket circuits with a 13A MCB.
 
20 amp should be fine supplying your 16amp socket as you say its covered in OSG part H3.
Out of interest have you hit mainly drains installing your earth rods for your EV chargers ?
 
20 amp should be fine supplying your 16amp socket as you say its covered in OSG part H3.
Out of interest have you hit mainly drains installing your earth rods for your EV chargers ?


I don't know! Scary every time though. Bought a cat scanner for cables but still!! 18th edition takes out the "where reasonably practical" bit. So expect a lot of People hitting utilities
 

Reply to 16 amp commando sockets. 20 amp mcb on site guide as maximum value mcb in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

We own a small, one bedroom flat (built 1989). An EICR inspection raised three C2 observations and recommendations: (A) The shower cable, and...
Replies
8
Views
4K
Hi I am a sparks from the 15th Ed, did 16, 17 and last year 18th. I am out of practice though as have been office based for 12+ years in a...
Replies
8
Views
2K
When caring out an EICR on a site I found that the 110 volt socket outlets were connected as three 2.5mm ring final circuits each protected by a...
Replies
17
Views
5K
B
Prefix - I've tried to post this in automotive, but it would not let me. This may be because I have not been recently active. Apologies if this is...
Replies
3
Views
3K
Ok, so I'm registered with Rated People. I don't use them very often but once or twice I have purchased a lead that has turned out to be very...
Replies
28
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock