Hi, I'm at a job where there is 4x16 amp sockets protected by 4x16 amp rcbos in a bollard, the customer now wants 6 amp rcbos cause he wants to limit what people are using can you do this? I suppose it will just trip if people use more than 6 amps
 
Yes.

You have answered your own question.

Do job, on certificate for circuit breaker change, note potential tripping caused by overload, submit with invoice ....
 
Hi, I'm at a job where there is 4x16 amp sockets protected by 4x16 amp rcbos in a bollard, the customer now wants 6 amp rcbos cause he wants to limit what people are using can you do this? I suppose it will just trip if people use more than 6 amps
What a load of bollards
 
Yes you can do this and yes the circuit breaker will trip if overloaded. It will be a safe circuit within the design parameters of the wiring regulations.
Is this a practical approach, no, because it is effectively designing the circuit to fail and causing a circuit breaker to trip regularly is not ideal as they will have a much shorter lifetime and so need replacement.
Informative signage would help but it is still not ideal from a practical perspective.

Murdoch has the better, shorter answer, cover yourself.
 
These are the bollards, and thanks guys much appreciated

IMG_3125.JPG


IMG_3126.JPG
 
Okay, stupid question time.

Is this installation designed to supply something like a market stall? The reason I ask is because I see C type RCBOs have been fitted.
 
Yeah ok :) I should have said what types and sizes of appliances ...

You'd think after all my time on here and years of wading through City and Guild's ambiguous syntax, I would have learned to construct a concise and specifically worded sentence wouldn't you ?

More the opposite .... its wading through the antiquities of BS 7671 that I hate
 

Reply to 16 amp socket help please in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Mobile home outdoor power supply is a pedestal that power to the mobile home plugs in much like an RV. The main power supply into the mobile home...
Replies
6
Views
844
Good morning, Ive a dry covered area by the side of the house where I’m wanting to some welding art, I bought a 200 amp tig welder , that says it...
Replies
3
Views
825
Hi, I'm installing a Hoover oven and would like a little help please. The oven code is HOC3158IN. The oven manual states "The power cable must...
Replies
9
Views
705
Hello, I have a hypothetical question (I'm an electrical engineer) to better understand RCBOs and how they are used in the USA. Let's say I would...
Replies
9
Views
1K
Hi guys, Rewired a unit where they make dentures, builder today has asked to install 16a commando socket with isolator (no problem) however...
Replies
23
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock