Discuss 16mm tails with 100amp fuse? in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
I am going to be changing the consumer unit in a house. The owner arranged to have an isolator switch fitted by N power (free of charge). Ive been to look at it and the guy has fitted it with 16mm tails. The customer was told that this was because the tails to the ccu are 16mm. But it has a 100amp fuse. I will be fitting a new 9.5kw shower and the cooker is electric as well as the usual ring main and lights ect. It is a 3 bed house. I was going to change the tails to the ccu to 25mm.

Am I correct in thinking that he should have fitted 25mm to the isolator switch? All the tables ive looked at say I am.
 
Is it actually a 100a Fuse? or does it just say that on the carrier, we only ever put a 60 or 80 in if it has 16mm tails when we change meters. Chances are its 60 or 80, It is on there side anyway so I wouldn't worry to much
 
I asked this the other day..

Just cause it says 100a, does it mean it is, ...... How can you check this,,, can you open the carrier?
 
no no no, im working on a house myself and the carrier says 100A and they looking to add another shower, but im thinking maybe isnt 100A in carrier..

whats mocopa?
 
If you look at the fuses tripping times then I think you will find they will blow at 1.5x in an hour so even a 60A would take 90 for an hour, I wouldn't honestly worry to much. If you were in western powers area, they only give out 80A's apart from special requests, other DNO's do either 60A or 100A.
 
nice info which i know but couldnt apply it or am i just lazy.. ty..

is there no way of checking tho....

is their a diffwerent in resistance if you measure between prongs
 
Nope, no way other then a physical check I'm afraid, so is a bona fide limitation!
Bear in mind if you are working in a flat and come accross a bright red fuse and carrier, this is a solid link! The fuse will be down at the incoming position to the building!
 
I tend to install 25mm tails on board changes these days as a matter of course tbh....always the possibility someone will request an upgrade to 100A in the future so at least it's sat ready waiting for it.
 

Reply to 16mm tails with 100amp fuse? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Locked
My house was built in the 1930s, The fuse in my service cut out is 60Amp and the wire coming from the street has a 16mm2 copper core(easy to see...
Replies
12
Views
570
Hi all, Customer has an extension and this compromises existing meter position, DNO is extending incomer and putting meter box on a different...
Replies
3
Views
402
Hello again, Was looking at installing yet another dedicated consumer box for my EV charger off the henley blocks and i noticed that a meter...
Replies
11
Views
2K
Hi all. I have been asked to take over a job an electrician has started, and has moved abroad. The house is a big mansion, with a 3PH supply...
Replies
49
Views
4K
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
814

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock