Discuss 17th regs in the Industrial Electricians' Talk area at ElectriciansForums.net

D

daisy

hi
can anyone help with equation in new regs page 59. reg 415.2.2
does R < 50 V/ Ia mean volts divided by amps. eg

for a 30 mA rcd. 50 divided 30 = 1.6ohms
or
for a 10 amp type b mcb. 50 divided 50 = 1.0 ohm

Thanks for your help
Daisy
 
hi
can anyone help with equation in new regs page 59. reg 415.2.2
does R < 50 V/ Ia mean volts divided by amps. eg

for a 30 mA rcd. 50 divided 30 = 1.6ohms
or
for a 10 amp type b mcb. 50 divided 50 = 1.0 ohm

Thanks for your help
Daisy

hi Daisy

the Ia means current causing operation of the protective device, so for a 30mA RCD, its IdeltaN which is 30mA

so divide 50 by 0.03 and you get 1667 ohms

now this figure is relevent trhoughout the regs

and there is a table of these figures in Part 4 (afew pages past the Max ZS tables)

So for example, a TT system protected by a 30mA RCD wold have a maximum rod impedence of 16667ohms

in a bathroom, if everything is on a 30mA rcd, and meets the disconnection times, you can dispense with supplementary bonding provided that any extraneous conductive parts odf have a resisrance of 1667 ohms or less to the main bonding

etc, etc

and what it all means is:

with a resistance of 1667 ohms, when a fault current of 30mA flowing (which is when the RCD trips) the fault voltage will be at 50V which is the maximum 'safe' level

job done;);););)
 
Hi - thanks for your replies, I'm having trouble sending a reply. The site is telling me I'm not logged in when I am, then I lose the message. I will try again later.
thanks Daisy.

Hi. Thanks again for your replies. Looking at shakey's answer to the equation confirms my doubts about this regulation. This reg (page 59) reg 415.2.2 is for checking the effectiveness of supplimentary equipotential bonding between accessable exposed conductive parts and extraneous conductive parts and the equation given is as above. This calculates, as Shakey has shown to 1667 ohms. (well, don't know about you but if I have cross bonded two accessable parts I would hope the resistance would be lower than that). In the old 16th edit the value recommended was 0.05 ohms or less. This regulation is also used in the locations containing a bath or showerpage 166 reg 701.415.2.See the note at the bottom of this reg.
Am I misreading this regulation? I would like your thoughts.Thanks Daisy.
 
Last edited by a moderator:
Hi - thanks for your replies, I'm having trouble sending a reply. The site is telling me I'm not logged in when I am, then I lose the message. I will try again later.
thanks Daisy.

Hi. Thanks again for your replies. Looking at shakey's answer to the equation confirms my doubts about this regulation. This reg (page 59) reg 415.2.2 is for checking the effectiveness of supplimentary equipotential bonding between accessable exposed conductive parts and extraneous conductive parts and the equation given is as above. This calculates, as Shakey has shown to 1667 ohms. (well, don't know about you but if I have cross bonded two accessable parts I would hope the resistance would be lower than that). In the old 16th edit the value recommended was 0.05 ohms or less. This regulation is also used in the locations containing a bath or showerpage 166 reg 701.415.2.See the note at the bottom of this reg.
Am I misreading this regulation? I would like your thoughts.Thanks Daisy.

yep Daisy, you're misreading it:p

it is NOT for checking the effectiveness of the supplementary bonding!

what it means is, for a bathroom, if extraneous conductive parts have a resistance of 1667 ohms or less to the main bonding AND all circuits on a 30mA RCD AND they all meet their disconnection times then supplemtary bonding is not required.

exposed conductive parts are already connected through the CPC

so if there is an earth fault on a bathroom circuit, the extraneous conductive parts can not reach a fault voltage higher than 50V before the RCD trips

and yes, it would normally be a lot lower!

and remember, if the resistance is a LOT higher (i.e. open circuit) then the chances are there is plastic pipework and it isnt an extraneous conductive part anyway!!! (and should NOT be supplementary bonded);)
 
Hi
Thanks Shakey.
I see what you mean by this not checking the supplementary bonding in this case.
Right then try this!
In that note (page166) which we have already mentioned we are asked to check between the extraneous parts and the main earthing terminal.As you have said this could be 1667 ohms what happens if it is a T.T system with an earth electrode resistance, including earthing conductor of say 100 ohms measured from the main earthig terminal. this would now take us above the max value of in this case a 30 mA RCD.
Thanks Daisy
 
Hi
Thanks Shakey.
I see what you mean by this not checking the supplementary bonding in this case.
Right then try this!
In that note (page166) which we have already mentioned we are asked to check between the extraneous parts and the main earthing terminal.As you have said this could be 1667 ohms what happens if it is a T.T system with an earth electrode resistance, including earthing conductor of say 100 ohms measured from the main earthig terminal. this would now take us above the max value of in this case a 30 mA RCD.
Thanks Daisy

ok Daisy, i can see your chain of thought, but you may becoming...erm..'confused' between earthing and bonding, as so many people do!!

so for a TT, protected by a 30mA, max Zs of 1667 ohms means it will disconect within the 50V

BUT of course the Zs is Ze (which we know is external) + (R1 + R2)

and of course R2 is the cpc resistance for your circuit from its extremity to the MET

and we know this is earthing, and is the fault path the earth fault current will take, and will take into account the exposed conductive parts

however, as you also no doubt know, the extraneous conductive parts are all about bonding, not earthing, and of course the bonding, (main or supplementary) are not considered to part of the earth fault current path

so consider an earth fault on a bathroom circuit (even on a TT system)

so a fault current is flowing through the exposed conductive part, through the CPC and back to the MET (and when it reaches a max of 30mA the RCD pops)

so lets say you are touching the extraneous conductive part (say a radiator) and the now live exposed condcutive part at the same time

if they were cross bonded they would be at the same potential, and you would be safe.

and if the resistance of the extraneous to the MET was say 1000ohms, then the fault current would have to decide to go the 'easy way' back through the low resistance R2 to the MET or the 'hard way' through YOU AND the 1000ohms extraneous path.

And of course, the exposed conductive part cant get above 50V fault voltage anyway, so you now have a max of 50V AND a 'high' resistance path between you and an electric shock. And of course this only until the RCD trips!

so your 100 ohms TT analogy would ONLY come into play IF there was an earth fault AND the CPC went open circuit

and of course, the definition of fault protection includes the words "under SINGLE fault conditions";);)

so yes, theoretically, IF the CPC failed, AND your extraneous had a resistance to the MET of 1667ohms AND the Ze through the earth electrode was 100 ohms AND (finally!) there was an earth fault then the fault voltage could rise marginally above 50V before the RCD tripped

BUT

to 'feel' that 50V you would have to be touching the extraneous AND exposed conductive parts at the same time:rolleyes:

AND we would now be outside the realms of fault protection (the reason the RCD was put there in the first place) because you would be under multiple fault conditions;)

hope this has helped

oh, and as with most of my posts

i just made all that up.......:p:confused:
 
Thanks Shakey.
Just what i thought ???
I like your point on the " single fault condition ".This is a term i have skipped over not paying any attention to.
I am working my way through the new regs so i am sure i will have more problems.
Thanks Daisy.
 
Thanks Shakey.
Just what i thought ???
I like your point on the " single fault condition ".This is a term i have skipped over not paying any attention to.
I am working my way through the new regs so i am sure i will have more problems.
Thanks Daisy.

you get any more problems Daisy, fire away

i am sure one of can help you out;)
 

Reply to 17th regs in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

I know how I was taught to test a RCD, 6 tests in all two no go, two under 300 mS and 2 under 40 mS with no load. But thinking about it not so...
Replies
7
Views
3K
I apologise for what must seem an elementary question to most of you: I have need to power a series of LED lamps (in total, up to 60). I am...
Replies
17
Views
1K
S
As I understand it, they should have their own dedicated RCD After asking Mr Google I found this reference fro 17th Edition 2010Low Voltage...
Replies
21
Views
5K
sintec
S
K
Hi, I have just fitted a New consumer unit as my accessment job to get registered. The layout is: 100amp isolation switch 6 amp RCBO for smoke...
Replies
17
Views
4K
I recall being taught that if you measure continuity between the MET and extraneous-conductive parts in a bathroom and, as a rule of thumb, it is...
Replies
35
Views
10K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock