Discuss 1mm cpc in ring mains in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

N

nrbspark

Hi guys my local authority have asked me to carry out some PIR's on some properties with regards to upgrading them to 17th edition. I suspect that the rings will be 2.5 t+e and will have a 1mm cpc, if left will the properties comply with a 1mm cpc using a 32 A mcb (obviously RCD protected) or will the mcb require downgrading ? Any help is appreciated ty
 
Check the Part P Document. its only a problem when protection is by a 30Amp Re-Wireable fuse. So long as they are MCB and RCD protected, as mentioned in other posts, its a code 4
 
It will be a code 4.....doesnt comply with Bs 7671.....you just need to record the defect but it will not on it's own result in a unsatisfactory.

Company I once worked for the QS sent the sheets back saying I could not say the the installation was satisfactory as Code 4's had been noted on test sheet so had to change it to unstatisfactory.
 
Last edited:
Company I once worked for the QS sent the sheets back saying I could not say the the installation was satisfactory as Code 4's had been noted on test sheet so had to change it to unstatisfactory.


That is strange, we were told on the 2391 course code 4's were not always Unsatisfactory, for example, the old green earth sleeving is a code 4, but you certainly wouldn't go around changing it all to green and yellow just to get a satisfactory on a PIR
 
2.5 t/e cpc went from 1.0 to 1.5 with the 15th edition which was around 1990 if I recall so only 20ish years.
A code 4 is a departure from the current regulations but does not imply the installation is unsafe therefore a code 4 cannot result in an unsatisfactory. If you consder the defect compromises the safety of the installation you must apply a code 1 or 2 and give an unsatisfactory verdict.
 

Reply to 1mm cpc in ring mains in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
Been looking at a CU change in a small office and would appreciate comments on the following. Office is supplied from the mains intake in the...
Replies
52
Views
6K
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K
Good afternoon all, today I experienced a near death electric shock. This happened on a single phase domestic property! I was carrying out a few...
Replies
15
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock