Discuss 2.5mm ring main and Celotex Insulation in the UK Electrical Forum area at ElectriciansForums.net

R

Roger Perkin

I am building a garden office and currently have 25mm Celotex in the walls. I am running the ring main around and then want to add some more Celotex.

My question is how much of an air gap do I need to leave for the ring main?
 
It is not so much how much air gap as what is the drop in current carrying capacity. Which in the case of 2.5mm² drops down to 17a (ish) in insulation thus reducing from 54a to 34a. How much load do you think is going on to the ring final circuit. I would say ring main but we have a pet rottweiler who will get cross if we do, he is right though!
 
The ccc of the live conductors ( iz) should not be less than 20amps in each leg of the ring final circuit.
See regulation 433.1.1 and 433.1.204
 
Last edited:
Interesting will check that (again) but umm well if the 2.5 is doubled up how do you read that? as in yes its drops to 17a ish but as it is doubled up it is 34a yes? No? Maybe, don't know...
Any conductor in a 32/30A ring final circuit should not be rated at less than 20A.
 
Interesting will check that (again) but umm well if the 2.5 is doubled up how do you read that? as in yes its drops to 17a ish but as it is doubled up it is 34a yes? No? Maybe, don't know...

No, the ccc of the conductor used to form the ring should not be less than 20A.
The cable is not doubled up, it is in a ring, the difference is subtle but it is different
 
OK so I need to ideally not leave any air gaps in the insulation but need to run the ring circuit in there - total load on the cable will be a laptop, 2 monitors, and a 1kw heater and iphone charger - that's it
 
OK so I need to ideally not leave any air gaps in the insulation but need to run the ring circuit in there - total load on the cable will be a laptop, 2 monitors, and a 1kw heater and iphone charger - that's it

What made you choose a ring circuit for a single office? It seems a bit over the top to me.
 
I thought it had to be a ring. It was only another 4m of cable to run it back no big deal - but just need to find out if I can bury the cable in the celotex or if I need to leave air around it?
 
Im assuming your talking about running cable in the cavity? where you have inserted celotex?

There is a requirement in the Building Regulations 2000, Approved Document C, 2004 Edition, Section 5: Walls, paragraph 5.13 b state that no cables other than electricity meter tails are to be located in the cavity of an external wall.
 
I thought it had to be a ring. It was only another 4m of cable to run it back no big deal - but just need to find out if I can bury the cable in the celotex or if I need to leave air around it?

Which regulation did you get that from?
That is up to you as the designer of the installation to decide, the insulation around the cable will affect the size of cable you use but you will need to do the calculation to work out how much bigger the cable will need to be.
 

Reply to 2.5mm ring main and Celotex Insulation in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello, I need to run a mains spur off the existing ring main in a domestic property. To get the double socket to the correct place I have to drill...
Replies
3
Views
242
Essentially I have a "normal" socket in a ring mains, i.e. one 2.5mm T&E going in and one 2.5mm T&E going out. I am looking to simply add two more...
Replies
2
Views
309
Good evening. Currently sorting out my girlfriend’s flat for rent. I’ve found all sorts of bad electrical work. Can anyone advise if this is an...
Replies
18
Views
1K
Hi guys I am looking to add 4 additional sockets for a room that is being converted for a bed ridden person. The room at present has no sockets in...
Replies
7
Views
1K
Hi all, I’ve had some good advice here in the last week or so which has made me ask a few more questions. 1. Ring main uses the old Red and Black...
Replies
10
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock