Discuss 2 spurs from a Junction Box....worried? in the UK Electrical Forum area at ElectriciansForums.net

Well yes... in your opinion it's not, in my opinion it is.

I could be swayed very easily with a regulation that prohibits it, but as far as I can tell, there is no such regulation. Thus as I've said, it may not be good practice (and we agree you and I are unlikely to use this method), but good practice is not the same as the regulations.
I'm not going to wave the white flag SC, but shall we agree to disagree?
 
I'm not going to wave the white flag SC, but shall we agree to disagree?

Hell no, this is a fight to the death :D

I think it's quite an interesting debate because it highlights yet another ambiguity in the regulations that appears to be based on what people consider to make up the regulations.

As I've said all along, personally I wouldn't do it unless I had absolutely no other choice because I don't consider it to be good practice, I much prefer to extend the ring onto new outlets because it provides better options for future changes and greatly reduces the risk of someone down the line adding a spur from a spur.

So yes, we can agree to disagree :)
 
Thing is I can to a degree agree with SC and Co. As it is essentially the same as running a ring and then spur off for every socket but I'm assuming that due to it being on a single point of the ring it's classed as 1 spur with 2 sockets on, even if the is no leg between the rfc and the jb.
 
Last edited:
Hell no, this is a fight to the death :D

I think it's quite an interesting debate because it highlights yet another ambiguity in the regulations that appears to be based on what people consider to make up the regulations.

As I've said all along, personally I wouldn't do it unless I had absolutely no other choice because I don't consider it to be good practice, I much prefer to extend the ring onto new outlets because it provides better options for future changes and greatly reduces the risk of someone down the line adding a spur from a spur.

So yes, we can agree to disagree :)
That's good it was going to be hard to find a suitable venue for the final battle.
 
Thing is I can to a degree agree with SC and Co. As it is essentially the same as running a ring and then spur off for every socket but I'm assuming that due to it being on a single point of the ring it's classed as 1 spur with 2 sockets on, even if the is no leg between the rfc and the jb.

And I think that's the crux of it... what constitutes a spur?

I believe a spur is the cable and what's on the end, not the point of origin.
 
And I think that's the crux of it... what constitutes a spur?

I believe a spur is the cable and what's on the end, not the point of origin.
Well this is the things isn't it.. Which further reinforces the inability of the iet and any other body relating being able to lay out the regulations in a understandable way. I'm not saying I would be able to do better or that they should do better because looking at just bs7671... That's a lot of information, how do you lay it out in a way that is understandable to everyone. This is where I agree with most saying "get a spark in" as a good spark should be able to discern safe from unsafe compliant to non compliant but also they know who to contact in cases like this. In any case, case closed I think no, its not compliant but yes it is safe as long as the op removes it or adapts it before leaving home permenately.
 
Interesting debate. I've found myself pondering different scenarios which I thought I would share. I don't know the answer but it would be interesting to hear members views.

1. Two wago boxes side by side on the ring (as mentioned earlier in the thread) with a spur from each. Would this be compliant?

2. Whilst installing example 1. You realise that you have a bigger box that will take all the wagos and save on one of the boxes. Would this be compliant?

3. Whilst installing example 2. You realise that you are using 4 way 222s and that you can remove the very short link between the wagos and put both spurs into the same one. So the wago is now maintaining the ring in place of the very short length of cable. Would this be compliant?

At what point, if any, does this become non compliant and why?
 
Interesting debate. I've found myself pondering different scenarios which I thought I would share. I don't know the answer but it would be interesting to hear members views.

1. Two wago boxes side by side on the ring (as mentioned earlier in the thread) with a spur from each. Would this be compliant?

2. Whilst installing example 1. You realise that you have a bigger box that will take all the wagos and save on one of the boxes. Would this be compliant?

3. Whilst installing example 2. You realise that you are using 4 way 222s and that you can remove the very short link between the wagos and put both spurs into the same one. So the wago is now maintaining the ring in place of the very short length of cable. Would this be compliant?

At what point, if any, does this become non compliant and why?

1. Yes
2. I guess
3. No
 
Op is it possible to run the original legs that you cut into on the rfc to a fcu then run both the 2.5mm to that and fix to a wall or something?
The OP hasn't come back with any evidence that he has actually spurred from the ring and no from a spur that already exists.
 
The OP hasn't come back with any evidence that he has actually spurred from the ring and no from a spur that already exists.
Well this is true and would be even worse obviously if they had spurred from a spur. op what's the situation can you confirm it's a leg off the rfc and not a spur that you've tapped into??
 
sorry pete. i have to agree with miss whiplash sparkychick.:D:D:D.
No need to be sorry Tel, we all have differing opinions. Out of interest which thread are you agreeing with, and tread carefully Mate, with the innuendos.
 
due to it being on a single point of the ring it's classed as 1 spur with 2 sockets on, even if the is no leg between the rfc and the jb
It's all defined by the iet in the regs
"Spur. A branch from a ring or radial final circuit."
So that is clear it refers to the cable rather than the point of connection.

While everyone is on the topic, i can't find anything in the regs that allows a lollipop circuit. I was trying to find out whether the wording would allow a figure of eight, but i can't find any reg allowing a lollipop, as a ring final circuit defines the whole circuit to be arranged as a ring. Any pointers?
 
New posts

Reply to 2 spurs from a Junction Box....worried? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, i live in a new build house where they builders have left a junction box on the outside of my house. In the junction box there is a 6mm twin...
Replies
14
Views
1K
Hi, Hopefully I haven't made an error but I was speaking with another electrician and he said standard junction boxes with screw terminals can no...
Replies
3
Views
860
Ok. Can you cut a ring in half, add junction box, then run a spur off it? I thought it had to be from a socket? Mate of mine wanted me to see if...
Replies
3
Views
775
Hi everyone, I've got an electrical ring circuit that looks somewhat like the drawing below, where the blue sockets are part of the main ring and...
Replies
2
Views
1K
Hi Everyone, Sorry in advance if this is a silly question. There is a junction box in my mother's kitchen, on the wall above her kitchen...
Replies
5
Views
959

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock