Discuss 2 way switching wiring issue in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
I’ve got Hall/landing 2 way switching.
Both switches recently replaced. I have a red cable on the 3 core that was initially in the common up and down. However the upstairs landing would only switch on/off from the bottom switch and then it didn’t switch on or off at all.

Taking the red out of the common means the upstairs light now switches on and off but a light next to it will only switch on if the upstairs landing is turned on.

Any ideas?

F4B32D35-3FDA-4926-84D3-6492814169DF.jpeg


7A47C5FD-E638-412E-9ECE-7D3AA39EABA1.jpeg
 
We have a couple of issues here before anyone can try and advise, one the chrome light switch has not been earthed and second the earths (bare wires) at the other switch are either not connected or cut off. The pic of the chrome switch is too unclear to see what is going on.
 
Last edited:
The picture isn’t great but the only wires in the 2 way are blue in L2 and yellow L1. There’s a common looped over from the switch next to it.
In its current state the it works. You can switch the landing light from the hall and the landing. However there is another light on the landing on a separate one way switch which now only works if the main landing light is turned on.
This other light does work if the red wire (currently out of the switch) is put in the common. However then the landing light is permenantly on and not switched.
 
what he said^^^^^^.you need the services of an electrician. should only cost about an hour's labour.
 
As above you need to get an electrician in or whoever installed the switches back. Which switch is upstairs (landing) and downstairs (hall)? What are the switches switching?
 
I’ve got Hall/landing 2 way switching.
Both switches recently replaced. I have a red cable on the 3 core that was initially in the common up and down. However the upstairs landing would only switch on/off from the bottom switch and then it didn’t switch on or off at all.

Taking the red out of the common means the upstairs light now switches on and off but a light next to it will only switch on if the upstairs landing is turned on.

Any ideas?

Yes, if you did the work yourself switch off the supply until an electrician has made it safe.
If you employed someone to do that then do the same but also seek legal advice as they have placed your life, and the lives of your family, at risk.
 
@gaz4701
Its a straight forward fix for an electrician, but as the other have said its not a job for you to tackle yourself, its not safe in its current state. Therefore its not just a case of putting the conductors back into their proper terminals but also making sure there is adequate fault & shock protection. As "westward10" said this takes priority over the correct operation of the switching arrangement.

I have seen it many times where some one has decided to DIY a new shinny metal 2 way switch not realising what requirements are necessary and end up mixing up the wiring arrangement also.
 

Reply to 2 way switching wiring issue in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi everyone I've moved into a flat and I've decided to replace the original electric switches and sockets with white ones. I've done them all...
Replies
3
Views
877
Strange on this, we are wiring an extension at the moment and I would like to 3 way the (currently 2 way) landing switch to the new bedroom so...
Replies
14
Views
644
Suggestions / solutions please anyone? I have a 2 way switch, Hall and Landing, power being fed on Landing. When the switch is turned on, the...
Replies
2
Views
534
Hi all was having a problem with lights work one min not next took ceiling rose cover off to find a stray black wire only terminal free is the...
Replies
15
Views
364
Hi All, Pretty comfortable with wiring lighting until I came across needing to install 2 way dimming with a Retractive switch. I didn’t even know...
Replies
3
Views
822

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock