Discuss 2 week old fryer fail in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

Reaction score
4
Still on a learning curve and need a bit of advice.

I had a chip fryer fail today passed the earth but then failed insulation on 500v setting class 1.
It’s only 2 weeks old. Fryer next to it passed fine. Then a pizza oven had the same problem!!

Any advice appreciated... well most of it ?
 
How much of a fail? I.e. what sort of IR result did it find?

It is not uncommon for heater elements in ovens to be troublesome for tripping RCD due to leakage if unused for a while and moisture absorbed, but they usually clear if run up to temperature (which can be problematic if the RCD keeps tripping...)
 
As above, sheathed heating elements can absorb moisture with disuse although new appliances are usually OK. When warmed up, the IR value tends to fall rapidly, then slowly rise back to and beyond the initial reading. Need specs and readings to comment further.
 

Reply to 2 week old fryer fail in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

Similar Threads

Hello, I am currently learning and have come across PAT testing an old chandelier. On modern lamps I would use the plug and probe on the...
Replies
1
Views
2K
Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Replies
20
Views
3K
DIY query Have narrowed down the source of an occasional trip to one light circuit which is a varilight v-pro master dimmer slave set up. This...
Replies
0
Views
450
I have a baffling problem with a newly-installed PIR floodlight and I'd like advice from the forum as to whether it's defective (and should be...
Replies
5
Views
581
Hello, I’ve got an issue driving me crazy and can’t get anyone to figure it out as it’s not their issue. We had a new extension, single rear...
Replies
9
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock