Discuss 2 x RCD's tripping in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
229
Hi guys, tried searching,whereby explanations have been given as to why a RCD will trip by a fault on a circuit that ISN'T electrically protected by the RCD tripping. Typically crossed neutrals or borrowed neutrals. I'm not into testing. Company I work for been called out to an EV bollard with 2 x 32 amp skts and 2 x Type A RCBO's protecting each socket within the bollard. Separate 65amp MCB SWA circuit supplying bollard. Socket 1 protected by Type A RCBO 1. Socket 2 protected by Type A RCBO 2.
However when skt 1 used RCBO 2 tripps! When socket 2 used RCBO 1 tripps! All internal wiring has been check out to ensure connected correctly ie no cross neutrals etc.
Bollard sited internally, TN-C-S earthing. On a temp basis TN-C-S removed and TT created at bollard. Made no difference. RCD's trip within about 5 mins when 1 x skt on load (about 30amps). The RCD's when tested by instruments are OK. As usual your thoughts appreciated.
 
When you say a separate 65A MCB SWA circuit to the bollard what do you mean , is it an additional supply ??
Perhaps a sketch or photos may be helpful...
 
Hi guys, tried searching,whereby explanations have been given as to why a RCD will trip by a fault on a circuit that ISN'T electrically protected by the RCD tripping. Typically crossed neutrals or borrowed neutrals. I'm not into testing. Company I work for been called out to an EV bollard with 2 x 32 amp skts and 2 x Type A RCBO's protecting each socket within the bollard. Separate 65amp MCB SWA circuit supplying bollard. Socket 1 protected by Type A RCBO 1. Socket 2 protected by Type A RCBO 2.
However when skt 1 used RCBO 2 tripps! When socket 2 used RCBO 1 tripps! All internal wiring has been check out to ensure connected correctly ie no cross neutrals etc.
Bollard sited internally, TN-C-S earthing. On a temp basis TN-C-S removed and TT created at bollard. Made no difference. RCD's trip within about 5 mins when 1 x skt on load (about 30amps). The RCD's when tested by instruments are OK. As usual your thoughts appreciated.

By Marconi May I ask for a little more information? Has this problem only recently arisen? Does it happen for all the EVs which are charged at the site? What size is the SWA and how long? Is there a separate CPC between the 65Amp MCB and the bollard? Are the RCBOs electronic types? Has there been any lightning recently nearby?

Some quick things to consider:

Are the SWA glands in good order and fitted correctly?

Are the RCBOs Functional Earths securely connected?

Are all connections, at both ends of SWA, especially for CPC and N, tight and good?

I am wondering whether the RCBOs are being tripped because of an effect somewhere between their input terminals and the MCB. What you describe might be due to the Functional Earth and associated internal circuitry detecting loss of N, loss of CPC, loss of supply or N-E fault upstream of the RCBOs.

Might you take some voltage readings, at the supply terminals of the RCBOs: L-N and N-CPC for off-load and on-load conditions and watch what happens to them until a trip occurs? And put them in a post for me to take a gander at and muse over?
 
Borrowed neutrals would possibly cause both RCD's to trip at the same time,however it could be a fault causing a neutral neutral fault, ie . 2 neutrals damaged and shorting together, if they trip individually then the chances are its a neutral to earth fault , but this may not be associated with the circuit connected to the socket ,as the earths and neutrals are linked together on there own bars , all earth all neutrals , the fault could be on another circuit which is causing the in balance , and the best way of finding this is to disconnect all the earths and neutrals and test each circuit until the fault is located ,so its get the tester out and start testing
 
Hi guys, tried searching,whereby explanations have been given as to why a RCD will trip by a fault on a circuit that ISN'T electrically protected by the RCD tripping. Typically crossed neutrals or borrowed neutrals. I'm not into testing. Company I work for been called out to an EV bollard with 2 x 32 amp skts and 2 x Type A RCBO's protecting each socket within the bollard. Separate 65amp MCB SWA circuit supplying bollard. Socket 1 protected by Type A RCBO 1. Socket 2 protected by Type A RCBO 2.
However when skt 1 used RCBO 2 tripps! When socket 2 used RCBO 1 tripps! All internal wiring has been check out to ensure connected correctly ie no cross neutrals etc.
Bollard sited internally, TN-C-S earthing. On a temp basis TN-C-S removed and TT created at bollard. Made no difference. RCD's trip within about 5 mins when 1 x skt on load (about 30amps). The RCD's when tested by instruments are OK. As usual your thoughts appreciated.


By Marconi With regards to this problem and the highlighted text above I understand the description to be the off load RCBO is the one which trips after an interval of around 5 mins but the on load RCBO remains set. Perhaps driverman could clarify please? It is the feature of the problem which most intrigues me.
 
By Marconi With regards to this problem and the highlighted text above I understand the description to be the off load RCBO is the one which trips after an interval of around 5 mins but the on load RCBO remains set. Perhaps driverman could clarify please? It is the feature of the problem which most intrigues me.
Yes, that is exactly it. However I'm a bit of a bystander with this. At the moment the RCBO's have been changed to type A RCD's and is all working fine. The situation is being constantly monitored.
 
Yes, that is exactly it. However I'm a bit of a bystander with this. At the moment the RCBO's have been changed to type A RCD's and is all working fine. The situation is being constantly monitored.

By Marconi Thank you. I will look out for any further developments and chip in my tuppence-worth if I see you post on it again. It is very interesting to me.
 

Reply to 2 x RCD's tripping in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

hi all come across a new build commercial office where radial circuits feeding electrak power track was protected by 32A RCBO at dist board and...
Replies
15
Views
1K
Cant get my head round this :( I understand N-E faults cause RCD's to trip, but I cant understand why on these 2 occasions, googled allover but...
Replies
13
Views
1K
An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K
Hi, I swapped a 2 gang switched socket for a 2 gang switchless socket with usb ports downstairs. I switched off all the power to the house by...
Replies
8
Views
781
I was wondering if someone might be able to help either confirm or change my understanding on the use of S-Type RCDs. I believe that they can be...
Replies
1
Views
660

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock