Discuss 20 amp double pole switches in the UK Electrical Forum area at ElectriciansForums.net

WallaceP

-
Arms
Reaction score
235
Hello,
Just wanted to share a fault I had today and was wondering if anyone else has come across it. So I wired a kitchen and the customer supplied the faceplates (I know...)
So after a lot more time explaining what they needed to buy and that a light switch would not work as an isolation switch for the oven(even tho they claimed that is how the electrician who wired their old house done it!)
Anyway, they called me back saying that the oven and dishwasher were tripping the RCD. I found that the 20a double pole gird switches must be switching the live before the neutral and because the new oven they bought have electronics in them this current must be wanted to return on the cpc and causing the RCD to trip.
The gridswitches were Varilight, which i would not have picked myself but they had already bought the other faceplates from this brand. I did not think they were a bad brand and I am fairly surprised with this fault and was wondering if it was more common than i realise.
 
Not one I've run into, though I don't install grid switches that often - and they usually don't get switched off very often. Is it repeatable - as in tripping every time the switch is turned on, and doesn't happen if the rcd is reset with switch on?

Varilight are a fairly decent brand - did they source them from a reputable supplier, or just buy them on ebay?
 
Hi,have you done all appropriate tests,to ensure this fault is the switch?

You would not want to obtain the best double pole switch in the world,only to find out there are other issues.

How are the grid switches configured,for these two machines?

...I bet it's easier to reset the RCD,than the clocks ...
 
All initial inspection was done at when the kitchen was wired. Today I rechecked polarity, earth loop, rcd ramp, rcd times, the end to end on the ring, resistance L-N (shorted at board) to each outlet.
The set up is kitchen ring with socket outlets 7 appliances on a 20amp switch each to a single socket. The fridge, freezer, cooker hood and wine chiller all work, but are very basic appliances, the oven, microwave and dishwasher are the ones causing the problem.
You would be able to switch on the grid switches maybe 1 in 3 times and not trip the RCD but if they are all on the RCD will reset. I have bypassed the neutral on the switch just now and it all works fine now, i could not get the rcd to trip when i turned the items on and off repeatedly
 
as liitlespark says. they are for isolation , not on/off switches.
 

Reply to 20 amp double pole switches in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I'm installing a Hoover oven and would like a little help please. The oven code is HOC3158IN. The oven manual states "The power cable must...
Replies
9
Views
645
I have just checked a double outlet and it trips at 18ma. It was supposed to be faulty. Washing machine had a bad heater which got replaced but...
Replies
10
Views
575
I'll start by saying - I have absolutely no intention of doing any wiring or anything electrical myself. You get someone professional to do a...
Replies
8
Views
835
Looking at instructions for installation for Baumatic BHI300 it requires a 20A Double pole (3mm separation) switched fused spur, I quote pretty...
Replies
3
Views
758
I need to replace a Hagar RCD (model number CN284U). This is a type AC RCD and I wish to replace it with a type A. The model number for the Type...
Replies
28
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock