Discuss 20 Amp DP switches in the Industrial Electricians' Talk area at ElectriciansForums.net

Amp David

-
Mentor
Arms
Reaction score
904
A 20 amp DP switch is rated to switch a max load of 20 amps right?

Being told this afternoon that they can only be installed on a circuit that is fused at <=20 amps.:whatchutalkingabout
 
im in agreement with you amp. ive used them in the birds mums house instead of a fused spur, to isloate the washing machine, and dishwasher. a standard domestic socket is only rated to 13A per outlet, yet they are often installed on a 32A MCB.
 
disagree. the 20A switch's load is limited to what you connect to it. obviously, you would not connect a load exceeding 20A.
 
so expanding on that. an 80A Main Switch in a CU protected by a DNO 100A fuse is a no no then?
 
Surely as long as a load of less than 20A is drawn through that switch, it doesn't matter what the MCB is rated at?

If you were using it as an isolator for a single 13 amp socket for example, you'd be fine IMO.

I've got a 20A DP in my kitchen which isolates the 13A socket for the washing machine under the counter. Doesn't make any sense that this wouldn't be compliant.
 
Last edited:
So connecting one to a circuit protected by a 30/32 amp fuse or breaker is not allowed even if used as a switch for a single socket ?

The units are to BS1363, exactly the same as a twin or single 13A socket outlet.

The switching is rated at 20 Amps.
 
There was a bit of a debate about this very subject not long ago in another thread....
http://www.electriciansforums.net/electrical-forum-general-electrical-forum/38029-grid-wiring-kitchen-ring.html

M
y argument was that if you're feeding a socket outlet that's going to have something plugged in then the plug top will be fused.

Therefore, having a fused spur aswell would be pointless and would lead to discrimination issues as you'd have 2 fuses in series.

I see no point in fusing a 20A switch which is never going to be handling more than 13A.
 

Reply to 20 Amp DP switches in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

Mobile home outdoor power supply is a pedestal that power to the mobile home plugs in much like an RV. The main power supply into the mobile home...
Replies
6
Views
826
when installing circuits protected my mcb's , i have always used the 80% rule. eg a lighting circuits where the load won't exceed 80% of the mcb...
Replies
2
Views
842
Hi, I'm installing a Hoover oven and would like a little help please. The oven code is HOC3158IN. The oven manual states "The power cable must...
Replies
9
Views
643
I recently rewired my laundry room with MC cable, 20 amp circuit. I installed an AFCI/GFCI combo switch. The gas dryer trips it as soon as I plug...
Replies
3
Views
723
Hi all We are hoping to upgrade our oven. We currently have a single integrated oven and a separate induction hob. Each has its own red switch...
Replies
0
Views
833

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock